Dear Jiashen,

1. *First question: Line resistance*
If you notice the last part of of Carlos's response to your question, it
has the answer;
*
*
*"The model used in Matpower is the standard pi one-line equivalent of a
three phase transmission line, with quantities in per-unit. This is
constructed from a base voltage equal to sqrt(3) times the phase voltage
and a base power equal to three times the per-phase power.  With this
choice of base quantities, the base impedance is equal to the per-phase
impedance. This is covered in most power systems analysis textbooks." *

What Carlos is trying to explain is that the pi one-line equivalent is per
phase, and so are resulting values. My understanding is that MATPOWER is
modeled in such a way that* *the resistance values are '*for only one of
the three conductors' *i.e. per phase.

2. *Second question: Line rating*
For the line rating, in my own understanding the line ratings are based on
3-phase values, i.e.* '**the total rating for 3 conductors connected in
parallel'* .

All the best


On 12 July 2013 10:25, Jiashen Teh <[email protected]> wrote:

> Dear Carlos,
>
> Thank you for pointing out, however, can you tell me what's the answer to
> my questions?
>
> Yours sincerely,
>
> Jiashen Teh
> PhD Student
> Electrical Energy & Power Systems Group, School of Electrical & Electronic
> Engineering
> Ferranti Building (B18), The University of Manchester, M13 9PL, United
> Kingdom
> Tel: +44 (0) 161 306 2263; Mobile: +44 (0) 792 322 4864
> ________________________________________
> From: [email protected] [
> [email protected]] on behalf of Carlos E
> Murillo-Sanchez [[email protected]]
> Sent: 12 July 2013 02:01
> To: MATPOWER discussion forum
> Subject: Re: conductor resistance and power rating (MVA)
>
> Dear Jiashen:
>
> The model used in Matpower is the standard pi one-line equivalent of a
> three phase transmission line, with quantities in per-unit. This is
> constructed from a base voltage equal to sqrt(3) times the phase voltage
> and a base power equal to three times the per-phase power.  With this
> choice of base quantities, the base impedance is equal to the per-phase
> impedance. This is covered in most power systems analysis textbooks.
>
> carlos.
>
> Jiashen Teh wrote:
> > Dear Dr Ray,
> >
> > Before asking my question, allow me to put us on the same level of
> > understanding.
> > If I am not mistaken, each transmission line in reality is actually
> > consists of 3 conductors connected in parallel.
> >
> > Hence, these are my 2 questions based on the above assumption:
> >
> > The resistance values in Matpower are
> > (a) the total resistance of 3 conductors connected in parallel?
> > or
> > (b)  the resistance for only one of the three conductors?
> >
> >
> > The line ratings in Matpower are
> > (a) the total rating for 3 conductors connected in parallel?
> > or
> > (b) the rating for only one of the three conductors?
> >
> >
> > Yours sincerely,
> >
> > Jiashen Teh
> > PhD Student
> > Electrical Energy & Power Systems Group, School of Electrical &
> > Electronic Engineering
> > Ferranti Building (B18), The University of Manchester, M13 9PL, United
> > Kingdom
> > Tel: +44 (0) 161 306 2263; Mobile: +44 (0) 792 322 4864
>
>
>
>
>


-- 