The VG column in the gen matrix is only for the power flow problem. It has no 
effect on the OPF problem.

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645





On Jul 23, 2013, at 5:16 PM, Yi Liang <[email protected]> wrote:

> From my understanding, 
> 
> For the AC electricity, the matter is not the absolute value of the voltage 
> angle, the differences between different bus voltage angles are what you want 
> to know. So people set one bus as the reference bus and usually set the angle 
> as 0.  
> 
> I believe that Vm here is from the mpc.bus, which I assume is the start point 
> value. 
> However, in mpc.gen, there is a column (column 6) indicates the voltage 
> magnitude setpoint (p.u.). It's in a file called caseformat. Or you can find 
> it in the manual. 
> 
> for the additional questions, usually, in real world, people are going to 
> control the voltage magnitudes. So, in matpower, you can go and check the 
> mpc.gen mentioned above to check the setpoints of generator voltages. 
> 
> Hope it helps, Correct me if I made any mistakes. 
> 
> Thanks,
> Yi Liang
> 
> 
> On Tue, Jul 23, 2013 at 3:54 PM, spyros gian <[email protected]> wrote:
> Thank you Dr Zimmerman.
>  
> I am running an ACOPF in matpower. In the mpc.bus I set for bus 13: Vm=1 , Va 
> = 0, type = 3.  
> So bus 13 is my reference bus. This means that in the results I will take 
> that voltage at bus 13 has an angle of 0 degrees, and a magnitude of 1 pu? 
> Ie , in your reply you wrote that in ACOPF, the reference bus determines the 
> voltage reference for the system. Does this mean, only the voltage_angle or 
> also the voltage_magnitude are determined ?
>  
> After running the ACOPF, I get for bus 13:  Voltage angle = 0 , 
> Voltage_magnitude = 1.05 pu.
> This shows me that bus13, being the reference bus in the ACOPF, only means 
> that its angle is equal to 
> the Va parameter in the mpc.bus matrix. And that its voltage magnitude is 
> determined in the ACOPF.
>  
> Do you agree with this?
>  
> Secondly, I would like to ask you : Is it compulsory that a bus equipped with 
> generators, has voltage magnitude >=1 pu in the ACOPF results? 
>  
> Thank you
>  
> From: [email protected]
> 
> Subject: Re: OPF on matpower
> Date: Tue, 23 Jul 2013 13:44:09 -0400
> To: [email protected]
> 
> 
> Shri is correct … with some *very* minor tweaks … the only bus type that 
> matters is the REF bus which determines the voltage reference for the system, 
> and the voltage angle at that bus is set to the corresponding value in the 
> bus matrix, which is usually set to 0, but need not be.
> 
> And, yes, the OPF solvers in MATPOWER do find locally optimal solutions that 
> are not guaranteed to be globally optimal. Theoretically, MATPOWER could find 
> different solutions depending on the algorithm, starting point, algorithm 
> parameters, etc. However, in my experience, it has been very difficult to 
> find multiple local optima. The one example I have been able to confirm has 
> nearly identical objective values and active power dispatches, with some 
> differences in voltage profile and reactive dispatch in a few buses.
> 
> My conjecture is that in most cases, especially for relatively small systems, 
> the solution found by MATPOWER is likely the global optimum or else something 
> extremely close to it. I hope to include in an upcoming version some 
> contributed code that will be able to confirm in some cases that a solution 
> is a indeed a global optimum.
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> 
> On Jul 23, 2013, at 1:05 PM, Shri <[email protected]> wrote:
> 
> 
> 
> On Jul 23, 2013, at 9:42 AM, spyros gian <[email protected]> wrote:
> 
> Dear Dr Zimmerman,
>  
> Running an OPF in matpower means that 
>  
> 1. Bus types play no role (eg slack, PV, PQ etc)
> Yes.
> 2. All values for Real Power generation and reactive power generation are 
> unknown
> Yes.
> 3. All values for bus_voltages and voltage phase angles in buses, are unknown 
> as well
> The voltage angle of the reference bus is fixed and set to 0.
> 4. As a result, all values for real and reactive power flows are unknown. 
> Yes.
> 5. Losses are unknown.
> Yes.
>  
> What is known : 
> 1. The resistance, reactance, admittance per unit / per conductor 
> 2. Values for Real and Reactive demand at each bus 
> 3. Limits on voltage magnitude , limits on real and reactive power generation
> 4. MVA limits on each line
> 5. Fuel cost for each generator.
> Yes for all
>  
> So my question is 
> a. Are the above correct for matpower ? 
> b. Since matpower uses a non-linear optimisation, is the result a local 
> minimum or a global minimum? 
>     (for the case of a cost-minimization OPF) ? i.e. the values for voltages, 
> reactive powers etc, are    
>     globally optimum or perhaps other optimum values for all the unknown 
> quantities exist ? 
> I believe most of the optimization tools, such as fmincon in Matlab, find a 
> local minimum.
> 
> Shri
>  
> Thank you,
> Spyros Gian
>  
>  
> 
> 
> 
> 
> -- 
> Yi Liang, Master Candidate
> 
> Room 403, Coordinated Science Laboratory
> Department of Electrical and Computer Engineering
> University of Illinois at Urbana Champaign
> 1308 W Main Street, Urbana, IL, 61801-2307 
> 

Reply via email to