Thanks for reply, Idris.
I'm sorry for replying to be late.

Today, I'll try column 3 and 4.

Before trying these, is base MVA 0.01MVA?
In journal which I read, here is base KVA = 10KVA, so I rewrite 0.01MVA.

After trying clumun 3,4 ,I report to you.


Takauya Koyanagi
[email protected]

----- Original Message -----
> Hi Takuya,
> Your power did not converged because the line parameters (R and X)you 
entered in column 3 and 4 of the branch matrix (mpc.branch) are in ohms 
instead of p.u.
> 
> Solution:
> 1. Select the right base MVA; 10MVA for an example
> 2. the operating voltage of the network is 12.66KV. this should be 
your base KV
> 3. Calculate the your base impedance based on 1 & 2 above
> 4. compute the equivalent per unit impedances for the R and X in 
column 3 and 4 respectively
> Then run your load flow again. It should converge.
> On the alternative, add the expression below before the bus matrix (
mpc.bus)
> 
> mpc.baseMVA = 10;
> mpc.baseKVA = 12.66;
> Baseimpedance=(mpc.baseKVA)^2/mpc.baseMVA;
> 
> Then after the branch matrix (mpc.branch) add 
> 
> mpc.branch(:,3:4)=mpc.branch(:,3:4)/Baseimpedance;
> 
> Then run your load flow again. It should converge.
> 
> Idris 
> >-----Original Message-----
> >From: [email protected] [mailto:bounce-
> >[email protected]] On Behalf Of ????
> >Sent: 12 September 2013 11:02
> >To: [email protected]
> >Subject: 69 bus distribution system
> >
> >I want 69 bus distribution system, so I make that.
> >
> >I collect 69 bus distribution datas. I referred to journal of 
attachment.
> >
> >I modify 'case_ieee30', and input branch and bus datas of 69 bus
> >distribution system.
> >
> >After makeing 69 distribution system, I implement 'runpf'. But 'runpf
'
> >didn't converged.
> >
> >I attach 69 distribution system which I made. What is wrong?
> >
> >If 69 distribution system will be completed, let's use it together.
> >
> >So I want advise. Please lend me your strength.
> >
> >Takuya Koyanagi
> >[email protected]
> 
> 
> 



Reply via email to