0.5 degree might be possible if the termination criteria for the power flow is 
rather large. If small termination tolerances do not improve the match, it must 
be a difference in modeling somewhere.

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Oct 16, 2013, at 11:40 PM, jiji aminudin <[email protected]> wrote:

> Hi
> 
> Thanks for the feedback, Ray. Now I know why the losses are different 
> (Question 1-anwered). For Question 3, I did use the same data for both 
> Matpower and the other software, but the voltage angle still not tally. At 
> base case, the difference is roughly <0.5 degree. Can I just ignore it? 
> 
> To other Matpower forum members, please, i really need a hand to answer 
> Question 2. I would appreciate if you could run the load flow for IEEE24 bus 
> and email me the result. Since I'm afraid the problem is not cause by 
> Matpower but from myself. Perhaps I did some errors during installation parts 
> (some of the tests failed) and I just want to check whether it affects the 
> results.
> 
> Thank you
> 
> On Tue, Oct 15, 2013 at 10:15 PM, Ray Zimmerman <[email protected]> wrote:
> On Oct 13, 2013, at 7:46 AM, jiji aminudin <[email protected]> wrote:
>> Dear all,
>> 
>> I’m using Matpower to run load flow for IEEE-24 bus system. I would 
>> appreciate if anybody can help me on the followings:
>> 
>> 1) I just wonder why the difference between buses’s sending power and 
>> buses’s receiving power (for branch) doesn’t tally with the resulted line 
>> losses? For example (please refer to highlighted area in the attachment), at 
>> branch 1, bus 1 is sending 11.94-j26.92MVA and bus 2 receives 
>> -11.94-j22.45MVA. Logically, the losses will be 0-j4.47MVA 
>> ([11.94-j26.92MVA]-[-11.94-j22.45MVA]). But, the resulted line loses 
>> connecting the two buses are 0.004+j0.02MVA. Is that possible?
>> 
>> 
> The losses that are reported are only the series losses (I^2 * Z) and do not 
> include the reactive power injected by the line-charging elements of the 
> transmission model. This is simply a matter of defining clearly which losses 
> you are including. You will notice that in the System Summary section of the 
> output, the Losses are reported separately from the Branch Charging.
> 
>> 2) Is anybody here working on the same system as I am? Can you help me to 
>> verify the result (please refer to attachment)? 
>> 
>> 3) I’ve compared the result with other load flow software. It seems that the 
>> voltage magnitude and active power losses do not differ much. But, the 
>> voltage angle and reactive power losses vary significantly. Isn’t all the 
>> results should be approximately the same? 
>> 
> The voltage angle results should be exactly the same assuming the input data 
> is identical. The loss numbers may be different if other load flow software 
> lumps the branch charging together with the series losses, otherwise they 
> should also be identical.
> 
> 
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 

Reply via email to