Thank you! Does two the case of two isolated busses ( busses that are
connected to each other but not to the remainder of the grid) counts for
isolated buses? Or only single buses do?


On Thu, Feb 20, 2014 at 3:37 PM, Abhyankar, Shrirang G. <[email protected]
> wrote:

>  I believe the power flow and OPF do work for islands provided you have
> reference bus in each of the islands. One possibility for the solver
> failure is the presence of isolated buses (buses that do not have any
> transmission lines connected) in the islands. If there are any isolated
> buses then you need to set its bus_type=4 in the bus data.
>
>  BUS_AREA field is only used for petty printing purposes, it is not used
> in the solution process.
>
>  Shri
>  From: Petr Kaplunovich <[email protected]>
> Reply-To: MATPOWER discussion forum <[email protected]>
> Date: Thu, 20 Feb 2014 15:15:40 -0500
> To: "[email protected]" <[email protected]>
> Subject: Case of islanding
>
>  I have a network with islanding (graph is not connected) and trying to
> run both DCOPF and DCPF on it. As I found in archives of this list, Prof.
> *Zimmerman *replied once that if each island has a reference bus
> (mpc.bus(i,2)=3) then both functions should work fine. However I keep on
> getting matrix singularity matlab error for DCPF function and "solution is
> primal infeasible" for DCOPF function.
>
>  So the questions are - do DCOPF and DCPF MATPOWER solvers still work for
> islanding cases? Any thoughts on why I may be getting this errors? Should I
> set BUS_AREA field?
>
>  Thank you!
> Petr
>
>