Sorry, I meant the GS column.

   Ray

On Mar 7, 2014, at 9:00 AM, Ray Zimmerman <[email protected]> wrote:

> Based on what I see below, it looks like the difference is from shunts. 
> Notice there are some non-zeros in the BS column of the bus matrix.
> 
>      Ray
> 
> 
> >> mpc=loadcase('case300’);
> >> mpopt=mpoption('OPF_ALG_DC',200,'OUT_BUS',0,'OUT_BRANCH',0,'OUT_ALL_LIM',0,'VERBOSE',2);
> >> r=rundcopf(mpc,mpopt);
> 
> MATPOWER Version 4.1, 14-Dec-2011 -- DC Optimal Power Flow
> MATLAB Interior Point Solver -- MIPS, Version 1.0, 07-Feb-2011
>  it    objective   step size   feascond     gradcond     compcond     
> costcond  
> ----  ------------ --------- ------------ ------------ ------------ 
> ------------
>   0     474427.12                0.119951         7750      6288.56           
>  0
>   1     706292.47     23.586  5.03366e-16     0.914459      1900.17     
> 0.488726
>   2     706811.13     2.8981  9.94131e-16  8.36768e-13       245.27  
> 0.000734348
>   3     706424.94     1.4629  7.36521e-16   0.00385424      86.8407  
> 0.000546389
>   4     706332.29    0.67175   5.0377e-16  1.13509e-12      12.8299  
> 0.000131144
>   5     706301.52    0.42584  5.94015e-16  7.43969e-13      2.32315  
> 4.35643e-05
>   6     706294.23    0.21314  3.77564e-16  6.39677e-13      0.49385  
> 1.03216e-05
>   7     706292.64    0.10513  3.77521e-16  9.14906e-13     0.113122  
> 2.26163e-06
>   8     706292.34   0.049447  3.14584e-16  5.36245e-13    0.0255032  
> 4.16802e-07
>   9     706292.31   0.019494  5.03323e-16  3.28603e-13   0.00481366  
> 5.00004e-08
>  10      706292.3  0.0044363  7.92828e-16  2.24905e-13  0.000608401  
> 2.12219e-09
>  11      706292.3 0.00028709   6.2915e-16  5.39439e-13  6.14459e-05  
> 9.09311e-12
>  12      706292.3 2.9243e-06   3.7749e-16  8.97475e-13  6.14465e-06  
> 1.31861e-15
>  13      706292.3 1.7543e-07  3.08677e-16  7.94211e-13  6.14465e-07  
> 1.64826e-16
> Converged!
> 
> Converged in 0.88 seconds
> Objective Function Value = 706292.30 $/hr
> ================================================================================
> |     System Summary                                                          
>  |
> ================================================================================
> 
> How many?                How much?              P (MW)            Q (MVAr)
> ---------------------    -------------------  -------------  -----------------
> Buses            300     Total Gen Capacity   32678.4           0.0 to 0.0
> Generators        69     On-line Capacity     32678.4           0.0 to 0.0
> Committed Gens    69     Generation (actual)  23527.1               0.0
> Loads            199     Load                 23525.8               0.0
>   Fixed          199       Fixed              23525.8               0.0
>   Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
> Shunts            17     Shunt (inj)             -1.2               0.0
> Branches         411     Losses (I^2 * Z)         0.00              0.00
> Transformers     107     Branch Charging (inj)     -                0.0
> Inter-ties         0     Total Inter-tie Flow     0.0               0.0
> Areas              1
> 
>                           Minimum                      Maximum
>                  -------------------------  --------------------------------
> Voltage Magnitude   0.929 p.u. @ bus 9033       1.073 p.u. @ bus 149 
> Voltage Angle     -17.48 deg   @ bus 528       59.16 deg   @ bus 7166
> Lambda P           40.03 $/MWh @ bus 7166      40.03 $/MWh @ bus 7049
> Lambda Q            0.00 $/MWh @ bus 1          0.00 $/MWh @ bus 1   
> 
> 
> 
> On Mar 6, 2014, at 11:31 AM, Victor Hugo Hinojosa M. <[email protected]> 
> wrote:
> 
>> Dear Dr. Zimmerman,
>> I run the DCOPF algorithm to solve the IEEE 300-bus system considering the 
>> default technical data for the system. Using the MIPS algorithm, the 
>> solution converges in 13 iterations with an objective function of 706292.30 
>> $/hr. When I analyze the solution, the sum of the power generation (23527.15 
>> MW) is bigger than the load power (23525.85 MW). The commands used are the 
>> following:
>> mpc=case300; mpopt=mpoption; mpopt=mpoption('OPF_ALG',200,'OUT_ALL',0); 
>> salida_matpower=dcopf(mpc,mpopt);
>> I’d like to know why there’s a difference of 1.3 MW 
>> (sum(salida_matpower.gen(:,2))-sum(mpc.bus(:,3))
>> )
>> Regards,
>> Vh