Have you tried using the voltages of one of the solved cases as a starting 
point for your original case that isn’t converging?

   Ray

> On Oct 20, 2014, at 9:48 AM, Simone Cochi <[email protected]> wrote:
> 
> Dear all,
> I trying to run a lf on a MV network. I treat all the transformers as
> simple branch. If I use the whole case file the load flow doesn't
> converge, instead if I remove the first branch, that is the HV/MV
> transformer, and put the slack bus on bus 2 (MV busbar of the
> substation), the load flow converge. Also if I decrease the
> transformer impedance of 10 the load flow does converge. The
> transformer is a 25 MVA machine with a short circuit voltage of 14,6%
> circa. The case file is attached if someone want to check.
> <mpc.mat>