Let’s start with 3 issues with your input data …

1. gen matrix should have 21 columns, not 10.
2. You have VMIN and VMAX columns in the bus matrix swapped.
3. You have ANGMIN and ANGMAX columns in the branch matrix swapped.

Fixing those things won’t make the OPF converge, but the power flow (which 
converges already) solution should give you some indicators of where to look. 
Namely, a minimum voltage magnitude of 0.742, to me indicates the need for a 
lot of additional VArs somewhere.

     Ray



MATPOWER Version 5.0, 17-Dec-2014 -- AC Power Flow (Newton)

 it    max P & Q mismatch (p.u.)
----  ---------------------------
  0         2.300e+00
  1         3.464e-01
  2         9.258e-02
  3         1.521e-02
  4         5.680e-04
  5         7.341e-07
  6         1.094e-12
Newton's method power flow converged in 6 iterations.

Converged in 0.01 seconds
================================================================================
|     System Summary                                                           |
================================================================================

How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------  -----------------
Buses             84     Total Gen Capacity    2805.0         348.4 to 1742.0
Generators        18     On-line Capacity      2805.0         348.4 to 1742.0
Committed Gens    18     Generation (actual)   1590.6             642.7
Loads             45     Load                  1388.6            1041.4
  Fixed           45       Fixed               1388.6            1041.4
  Dispatchable     0       Dispatchable          -0.0 of -0.0      -0.0
Shunts            29     Shunt (inj)             -0.0             276.9
Branches         109     Losses (I^2 * Z)       202.04            763.39
Transformers       0     Branch Charging (inj)     -              885.2
Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas              1

                          Minimum                      Maximum
                 -------------------------  --------------------------------
Voltage Magnitude   0.742 p.u. @ bus 58         1.052 p.u. @ bus 13  
Voltage Angle    -111.02 deg   @ bus 43         8.82 deg   @ bus 4   
P Losses (I^2*R)             -                 20.92 MW    @ line 55-67
Q Losses (I^2*X)             -                 53.65 MVAr  @ line 55-67




> On Jan 9, 2015, at 11:41 AM, Zeya Aung [11547809d] <[email protected]> 
> wrote:
> 
> Hi all
> 
> I’ve tried FAQ #5 - still no convergence. Please help. Attached are the excel 
> file and code to convert into matpower structure. Many thanks.
> 
> 
>       
> ---------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
>        Disclaimer:
> 
> This message (including any attachments) contains confidential information 
> intended for a specific individual and purpose. If you are not the intended 
> recipient, you should delete this message and notify the sender and The Hong 
> Kong Polytechnic University (the University) immediately. Any disclosure, 
> copying, or distribution of this message, or the taking of any action based 
> on it, is strictly prohibited and may be unlawful.
> 
> The University specifically denies any responsibility for the accuracy or 
> quality of information obtained through University E-mail Facilities. Any 
> views and opinions expressed are only those of the author(s) and do not 
> necessarily represent those of the University and the University accepts no 
> liability whatsoever for any losses or damages incurred or caused to any 
> party as a result of the use of such information.
> <Myn-Matpower.xlsx><mepe_case.m>
> 
> Best
> Zeya
> 

Reply via email to