Thank you very much Ray, that your reply is detailed. I will work with it and let you know the results. On 21 Jan 2015 20:20, "Ray Zimmerman" <[email protected]> wrote:
> 1. The get_losses function itself is pretty clearly documented (see > Section 9.2.4 in the User’s Manual > <http://www.pserc.cornell.edu/matpower/manual.pdf>) so hopefully there’s > no confusion there. The LSF calculations in t/t_get_losses.m are specific > to the power flow, not the OPF, in that they assume fixed generator > voltages and a specific slack bus, etc. > > 2. There should be no difference, simply that get_losses() is more > convenient than pulling code out of printpf() to compute it yourself. > > 3. In t/t_get_losses.m I compute the loss sensitivities numerically, by > doing small (epsilon) perturbations of the load at each bus and recording > the corresponding proportional change in losses. That’s what a “sensitivity > factor” means. Then I compare this LSF matrix computed by numerical > perturbation with the one I computed analytically to test that the latter > is correct. > > Ray > > > On Jan 20, 2015, at 12:22 PM, nivedita arunachalam < > [email protected]> wrote: > > Dear Ray, > I have some doubts regarding the loss sensitivity factor > calculations you sent me. > 1. Is it for opf calculation alone? > 2. I work with normal runpf operations and I get power loss by calling > them from printpf (sum(real losses)). Then what is the difference in your > get loss file and direct values. > 3. Why do you use epsilon values in lsf caculation, what formula does it > represents? > > Kindly reply me... > > >