Thank you for your answer.

Is there a way to limit both current and apparent power?

Thank you,


Gamze

________________________________
> From: [email protected] 
> Subject: Re: Branch flow limits in OPF 
> Date: Wed, 25 Mar 2015 11:03:03 -0400 
> To: [email protected] 
> 
> By default, the “flow” constraint in the AC OPF is on apparent power 
> (in the DC OPF, it’s active power), not on current, which probably 
> explains what you are seeing. See the 'opf.flow_lim' option to change 
> the default. 
> 
> Ray 
> 
> On Mar 25, 2015, at 4:55 AM, Gamze Dogan 
> <[email protected]<mailto:[email protected]>> wrote: 
> 
> Dear all, 
> 
> 
> I have a question regarding the power flow limits in the OPF. The flow 
> is limited by the branch value rateA. 
> 
> 
> I wanted to calculated the pourcentage of flow in my lines after the 
> OPF succeeded. I did it this way: 
> 
> 
> V(d,1) = results.bus(d, 8) * exp(1j * results.bus(d, 9)*pi/180); 
> 
> 
> [Ybus, Yf, Yt] = makeYbus(mpz); 
> 
> 
> Ifrom= Yf*V; 
> 
> 
> pourcentage_line(d) = ( abs(Ifrom) (d) * results.baseMVA) / 
> results.branch(d,6) *100; 
> 
> 
> First, could you tell me if this is correct? 
> 
> Secondly, I have trouble interpreting the results as at the end of my 
> OPF I get pourcentage of flows higher than 100%, for me as the flow has 
> been limited to the rate A value, I sould not get flows higher than 
> 100%. 
> 
> Thank you for any help on the subject, 
> 
> Regards, 
> 
> 
> Gamze 
> 
>                                         