Short answer: Yes. It’s called an optimal power flow.

Long answer: The power flow problem computes a set of unknowns (flows, voltage 
angles, some voltage magnitudes, some reactive injections, etc) from a set of 
specified quantities (active injections, generator voltage magnitudes, etc.). 
By definition, the flows computed by this problem may violate limits. When you 
say you want to “activate thermal lims in pf”  you are implicitly saying that 
if a limit would be violated by the simple power flow solution you want to 
adjust some input parameter(s) to prevent that. There are typically an infinite 
number of ways to make these adjustments and satisfy the constraints. So, which 
input parameters are available for adjustment? And what criteria should be used 
to choose which adjustments to make? You now need a problem formulation that 
formalizes your answer to those questions. The optimal power flow with 
appropriate constraints and costs is precisely such a formulation. To limit the 
adjustments to only those you want, you may need to constrain some of the 
variables (voltages, dispatches, etc) to the desired values, as opposed to the 
ranges used for a typical OPF, but the problem formulation is the correct one, 
you just need to carefully specify the input parameters so it solves the 
problem you want.

   Ray


> On May 6, 2015, at 10:50 AM, Απόστολος Αρσενόπουλος <[email protected]> 
> wrote:
> 
> Hi all,
> Is there a way i can activate thermal lims in pf??
> 
> Thank you,
> AA
> 
> 