Hi Dr.Zimmerman and Robert,

I understand that Matpower can't work with an unbalanced three phase
circuit. For this example, I'm only working with the A phase leg of the
circuit. I'm just not sure how to setup the connection between nodes
correctly.

Thank you
Thai
On Jun 19, 2015 4:48 AM, "Robert Spiewak" <[email protected]>
wrote:

> Thai,
>
> You cannot aproximate unbalanced system consited of   branches and loads
> with 3W+N+G (three-phase, neutral and ground) via positive sequence solver
> like MATPOWER. The principle of methodology (NR) assumes symmetry in the
> system. Symmetry in branch impedances, loads and generation sources.
>
> Best Regards,
>
> Robert Spiewak
>
> > On Jun 19, 2015, at 08:18, Ray Zimmerman <[email protected]> wrote:
> >
> > MATPOWER does not model unbalanced 3-phase systems, and without a lot of
> work to refresh my memory, I’m not comfortable commenting on the
> possibility of a good single-phase approximation in your case.
> >
> > Maybe someone else can comment.
> >
> >    Ray
> >
> >
> >
> >> On Jun 18, 2015, at 8:24 PM, Thai Tran <[email protected]> wrote:
> >>
> >> Hi Dr.Zimmerman,
> >>
> >> I'm new to matpower so please excuse me if this is a silly question.
> >>
> >> I'm trying to use matpower to calculate power flow for a distribution
> grid. This circuit has power coming from a substation on 12.47 kV three
> phase line. Single phase transformers tap off the three phase line and step
> the voltage down to 120V to serve houses in the circuit. In matpower,
> transformers are modeled as a branch, how should I model the connections in
> my circuit?
> >>
> >> For example:
> >> substation is connected to transformer 1 which is then connected to 5
> loads. In the circuit model it would be
> >> substation -> transformer
> >> transformer -> load 1
> >> ...
> >> transformer -> load 5
> >>
> >> Should I model this in the branch matrix as
> >>
> >> substation(node 1) -> load 1 (node 2)
> >> ...
> >> substation(node 1) -> load 5 (node 6)
> >> load 1(node 2) -> load 2 (node 3)
> >> ...
> >> etc.
> >>
> >>
> >> Also since the transformer step the voltage level from 12.47kV to 120V,
> which level should I use to calculate my p.u impedance?
> >> Thank you
> >> Thai
> >
> >
> >
> >
>
>
>