Thanks Sh. Ji Chen for your kind information.

A dynamic data for a test network mainly include detailed modeling of
Generator (Exciter, PSS, Turbine/Governor) and Load (Constant ZIP -
impedance/current/power modeling) entities.

For your kind information, a dynamic data for the IEEE 39 bus test system
(New England) has been provided here:
http://www.sel.eesc.usp.br/ieee/IEEE39/New_England_Reduced_Model_(39_bus_system)_MATLAB_study_report.pdf

However, Load modeling can assumed as ZIP and set proper gain constants. In
the case of generator data, at least, the following details has to be
prepared, particularly the *Generator dynamic data (Unit No. xd  xdd
xddd Td0d Td0dd xq  xqd xqdd  Tq0d Tq0dd H D*.
=======================
*Generator dynamic data:*
Unit No. xd  xdd xddd    Td0d    Td0dd   xq  xqd xqdd    Tq0d    Tq0dd   H
  D

*Generator AVR parameters:*
Unit No. TR KA TA TB TC Vsetpoint EfdMax EfdMin

*PSS parameters:*
Unit No. K TW T1 T2 T3 T4 VP SSMax VP SSMin

*Generator setpoint data (Governor Model)*
Unit No. Pset point
=======================


Even in the case of *Generator dynamic data (*Unit No. xd  xdd xddd Td0d
Td0dd xq  xqd xqdd  Tq0d Tq0dd H *D), *we can assume either any of
generator model ( 2.2 model,  1.1 model or classical model), but the
setting of H and D indeed depends on the number of units connected together
in a power plant. Therefore, in order to generate a hypothetical data for
detailed modeling of a network dynamic data, I would request others to help
in setting of appropriate assumptions to the above data, particularly the
Generator dynamic data, for IEEE 118 or other higher sized networks.

Thanks in advance.



Sent with MailTrack
<https://mailtrack.io/install?source=signature&lang=en&[email protected]&idSignature=22>

--
with Regards
----------------------------------------------------
Gelli Ravikumar
Research Scholar (Ph.D),
Field Computations Lab,
Dept. of Electrical Engineering,
IIT Bombay, Powai, Mumbai 400076
Ph: 022-2576 4424, 089 765 983 96
My publications: http://tinyurl.com/gelliPapers

Gandhian Young Technological Innovation Award - 2013
POSOCO Power System Award: PPSA - 2013
IITB PhD Executive Member - 2013-14
IITB SARC Core Technical Member - 2014-15



On Mon, Dec 14, 2015 at 7:32 AM, Ji Chen <[email protected]> wrote:

> Dear Gelli,
>
> I think the change scanrios of the system loads should be set first.
> Then states at each time can be get by the power flow calculation.
>
> Ji
>
>
> At 2015-12-14 03:56:04, "Gelli Ravikumar" <[email protected]>
> wrote:
>
> Dear Sir/s,
>
> Is there a dynamic data available to the 118 Bus test case? If available
> please let me know and if not available, please let me know whether there
> is any provision to yield a hypothetical dynamic data from the steady-state
> data (http://www.ee.washington.edu/research/pstca/).
>
> Thanks in advance.
>
>
>
> --
> with Regards
> ----------------------------------------------------
> Gelli Ravikumar
> Research Scholar (Ph.D),
> Field Computations Lab,
> Dept. of Electrical Engineering,
> IIT Bombay, Powai, Mumbai 400076
>
>
>
>
>
>
> Sent with MailTrack
> <https://mailtrack.io/install?source=signature&lang=en&[email protected]&idSignature=22>
>
>
>
>
>

Reply via email to