sir
i am using price sensitive loads concept.i select the bus 4th as my
dispatchable load.before converting the loads to dispatchable the LMP at
the 4th bus is 40.19$/MWh.now i set the curtailble price at 38 as
 mpc=loadcase('case14m');
>> mpc0=load2disp(mpc,'m',4,38);
>> runopf(mpc0)

MATPOWER Version 5.0b1, 01-Jul-2014 -- AC Optimal Power Flow
MATLAB Interior Point Solver -- MIPS, Version 1.0.2, 01-Jul-2014
Converged!

Converged in 0.10 seconds
Objective Function Value = 6190.15 $/hr
================================================================================
|     System Summary
    |
================================================================================

How many?                How much?              P (MW)            Q (MVAr)
---------------------    -------------------  -------------
 -----------------
Buses             14     Total Gen Capacity     772.4         -52.0 to 148.0
Generators         5     On-line Capacity       772.4         -52.0 to 148.0
Committed Gens     5     Generation (actual)    220.2              71.2
Loads             11     Load                   211.2              77.4
  Fixed           10       Fixed                211.2              77.4
  Dispatchable     1       Dispatchable           0.0 of 47.8      -0.0
Shunts             1     Shunt (inj)             -0.0              20.7
Branches          20     Losses (I^2 * Z)         8.97             38.85
Transformers       3     Branch Charging (inj)     -               24.3
Inter-ties         0     Total Inter-tie Flow     0.0               0.0
Areas              1

                          Minimum                      Maximum
                 -------------------------  --------------------------------
Voltage Magnitude   1.011 p.u. @ bus 3          1.060 p.u. @ bus 1
Voltage Angle     -13.69 deg   @ bus 14         0.00 deg   @ bus 1
P Losses (I^2*R)             -                  2.72 MW    @ line 1-2
Q Losses (I^2*X)             -                  8.30 MVAr  @ line 1-2
Lambda P           35.84 $/MWh @ bus 1         40.03 $/MWh @ bus 3
Lambda Q           -0.08 $/MWh @ bus 1          0.56 $/MWh @ bus 14

================================================================================
|     Bus Data
    |
================================================================================
 Bus      Voltage          Generation             Load
 Lambda($/MVA-hr)
  #   Mag(pu) Ang(deg)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)     P
 Q
----- ------- --------  --------  --------  --------  --------  -------
 -------
    1  1.060    0.000*   184.04      0.00       -         -
 35.838  -0.084
    2  1.041   -3.889     34.80     25.44     21.70     12.70     37.398
  -
    3  1.011  -10.790      1.33     28.24     94.20     19.00     40.026
  -
    4  1.018   -7.626       -         -              0.00*    -0.00*
38.762   0.161
    5  1.019   -6.692       -         -               7.60      1.60
 38.380   0.220
    6  1.060  -12.021      0.00      9.97     11.20      7.50       38.386
    -
    7  1.048  -10.804       -         -         -         -
  38.787   0.133
    8  1.060  -10.804      0.00      7.52       -         -
38.787     -
    9  1.045  -12.468       -         -            29.50     16.60
 38.802   0.202
   10  1.040  -12.680       -         -            9.00      5.80
 38.950   0.308
   11  1.046  -12.482       -         -            3.50      1.80
 38.795   0.225
   12  1.045  -12.873       -         -             6.10      1.60
39.007   0.207
   13  1.040  -12.934       -         -             13.50      5.80
 39.200   0.343
   14  1.024  -13.692       -         -             14.90      5.00
39.800   0.559
                        --------  --------  --------  --------
               Total:    220.17     71.16    211.20     77.40

================================================================================
|     Branch Data
   |
================================================================================
Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 *
Z)
  #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q
(MVAr)
-----  -----  -----  --------  --------  --------  --------  --------
 --------
   1      1      2    125.50     -6.03   -122.78      8.50     2.718
 8.30
   2      1      5     58.54      6.03    -56.86     -4.39     1.685
 6.96
   3      2      3     64.90      1.90    -63.07      1.21     1.834
 7.73
   4      2      4     39.83      0.18    -38.98     -1.19     0.853
 2.59
   5      2      5     31.15      2.16    -30.63     -4.25     0.518
 1.58
   6      3      4    -29.80      8.03     30.43     -7.74     0.632
 1.61
   7      4      5    -37.01      9.82     37.19     -9.22     0.189
 0.60
   8      4      7     28.90     -2.65    -28.90      4.28     0.000
 1.63
   9      4      9     16.65      1.76    -16.65     -0.35     0.000
 1.41
  10      5      6     42.69     16.26    -42.69    -11.86     0.000
 4.40
  11      6     11      6.48      4.18     -6.43     -4.08     0.050
 0.11
  12      6     12      7.69      2.60     -7.62     -2.45     0.072
 0.15
  13      6     13     17.31      7.54    -17.10     -7.12     0.210
 0.41
  14      7      8     -0.00     -7.43      0.00      7.52     0.000
 0.09
  15      7      9     28.90      3.15    -28.90     -2.30     0.000
 0.85
  16      9     10      6.09      3.58     -6.08     -3.55     0.015
 0.04
  17      9     14      9.96      3.20     -9.83     -2.93     0.127
 0.27
  18     10     11     -2.92     -2.25      2.93      2.28     0.010
 0.02
  19     12     13      1.52      0.85     -1.51     -0.85     0.006
 0.01
  20     13     14      5.12      2.17     -5.07     -2.07     0.049
 0.10
                                                             --------
 --------
                                                    Total:     8.968
38.85

================================================================================
|     Voltage Constraints
   |
================================================================================
Bus #  Vmin mu    Vmin    |V|   Vmax    Vmax mu
-----  --------   -----  -----  -----   --------
    1      -      0.940  1.060  1.060   518.860
    6      -      0.940  1.060  1.060    72.456
    8      -      0.940  1.060  1.060    79.294

================================================================================
|     Generation Constraints
    |
================================================================================
 Gen   Bus                Active Power Limits
  #     #    Pmin mu    Pmin       Pg       Pmax    Pmax mu
----  -----  -------  --------  --------  --------  -------
   4     6    1.614      0.00      0.00    100.00      -
   5     8    1.213      0.00      0.00    100.00      -

Gen  Bus              Reactive Power Limits
 #    #   Qmin mu    Qmin       Qg       Qmax    Qmax mu
---  ---  -------  --------  --------  --------  -------
  1    1   0.084      0.00      0.00     10.00      -

================================================================================
|     Dispatchable Load Constraints
   |
================================================================================
Gen  Bus               Active Power Limits
 #    #   Pmin mu    Pmin       Pg       Pmax    Pmax mu
---  ---  -------  --------  --------  --------  -------
  6    4     -      -47.80     -0.00      0.00    0.351

Gen  Bus              Reactive Power Limits
 #    #   Qmin mu    Qmin       Qg       Qmax    Qmax mu
---  ---  -------  --------  --------  --------  -------
  6    4   4.868      0.00      0.00      3.90      -




my doubt is when i set the price at 45 more than the price 40.19 which i
get in normal power flow then the load is not curtailed.
1.the load should be curtailed for prices more than the marginal cost.but
here the load is curtailed for less prices.why and what is the concept
behind that.