Hi Jose,
Thanks for reminder. I didn’t know this option before. It solved my question.
So how do we know which PV bus, is there is any, is converted to PQ bus after 
using ENFORCE_Q_LIMS option 1 or 2?

Wenlei

From: [email protected] 
[mailto:[email protected]] On Behalf Of Jose Luis Marin
Sent: Thursday, March 24, 2016 3:57 AM
To: MATPOWER discussion forum <[email protected]>
Subject: Re: PV bus generator reactive power exceeding limits


Quick question, did you use the option pf.enforce_q_lims?  (see Table C-2 in 
the manual)

Also, be aware that options 1 and 2 may yield different solutions, in general.

--
Jose L. Marin
Grupo AIA


On Thu, Mar 24, 2016 at 6:08 AM, Bai, Wenlei 
<[email protected]<mailto:[email protected]>> wrote:
Dear Ray,
I’ve encountered a situation: the real power and voltage are specified in PV 
buses, and as I run the load flow on modified 30 bus case, somehow the reactive 
power of PV bus are exceeding the limits. Some even exceed the negative limits.
The thing is the reactive power demand of the load and system isn’t large.  Can 
you see what might be wrong?

Blessings,
Wenlei