Hi Jose, Thanks for reminder. I didn’t know this option before. It solved my question. So how do we know which PV bus, is there is any, is converted to PQ bus after using ENFORCE_Q_LIMS option 1 or 2?
Wenlei From: [email protected] [mailto:[email protected]] On Behalf Of Jose Luis Marin Sent: Thursday, March 24, 2016 3:57 AM To: MATPOWER discussion forum <[email protected]> Subject: Re: PV bus generator reactive power exceeding limits Quick question, did you use the option pf.enforce_q_lims? (see Table C-2 in the manual) Also, be aware that options 1 and 2 may yield different solutions, in general. -- Jose L. Marin Grupo AIA On Thu, Mar 24, 2016 at 6:08 AM, Bai, Wenlei <[email protected]<mailto:[email protected]>> wrote: Dear Ray, I’ve encountered a situation: the real power and voltage are specified in PV buses, and as I run the load flow on modified 30 bus case, somehow the reactive power of PV bus are exceeding the limits. Some even exceed the negative limits. The thing is the reactive power demand of the load and system isn’t large. Can you see what might be wrong? Blessings, Wenlei