Hi,
I am using MATPOWER 5.1.

I am trying to run opf for a 5 bus system mentioned in a book by "Stagg and
El-Abiad".

Following is my input system data:

function mpc = case5Stagg
%CASE5Stagg This represents the 5 bus system in Stagg El-Abiad book

%% MATPOWER Case Format : Version 2
mpc.version = '2';

%%-----  Power Flow Data  -----%%
%% system MVA base
mpc.baseMVA = 100;

%% bus data
% bus_i type Pd Qd Gs Bs area Vm Va baseKV zone Vmax Vmin
mpc.bus = [
1   3   0   0   0   0   1   1.05    0   230 1   1.05    0.95;
    2   2   20  9.7   0   0   1   1   0   230 1   1.05    0.95;
    3   1   45  22    0   0   1   1   0  230  1   1.05    0.95;
    4   2   40  19    0   0   1   1   0   230 1   1.05    0.95;
    5   1   60  29    0   0   1   1   0   230 1   1.05    0.95;
];

%% generator data
% bus Pg Qg Qmax Qmin Vg mBase status Pmax Pmin Pc1 Pc2 Qc1min Qc1max Qc2min
Qc2max ramp_agc ramp_10 ramp_30 ramp_q apf
mpc.gen = [
1 100 20 100 -100 1 100 1 125 20 0 0 0 0 0 0 0 0 0 0 0;
2 80 20 100 -100 1 100 1 125 20 0 0 0 0 0 0 0 0 0 0 0;
    4   0   50  50  0   1   100 1   0   0   0 0 0 0 0 0 0 0 0 0 0;
];

%% branch data
% fbus tbus r x b rateA rateB rateC ratio angle status angmin angmax
mpc.branch = [
1 2 0.02    0.06 0.03 180 180 180 0 0 1 -360 360;
    1   3   0.08    0.24    0.025   180 180 180 0   0   1   -360    360;
    2   3   0.06    0.18    0.02    180 180 180 0   0   1   -360    360;
    2   4   0.06    0.18    0.02    180 180 180 0   0   1   -360    360;
    2   5   0.04    0.12    0.01    180 180 180 0   0   1   -360    360;
    3   4   0.01    0.03    0.01    180 180 180 0   0   1   -360    360;
    4   5   0.08    0.24    0.025   180 180 180 0   0   1   -360    360;
];

%%-----  OPF Data  -----%%
%% generator cost data
% 1 startup shutdown n x1 y1 ... xn yn
% 2 startup shutdown n c(n-1) ... c0
mpc.gencost = [
2 0 0 3   0.0420 7.50 75;
2 0 0 3   0.0420 7.50 75;
    2   0   0   3   0   0   0;
    2   0   0   3   0.0043  -0.0383 0.2992;
    2   0   0   3   0.0043  -0.0383 0.2992;
    2   0   0   3   0   0.1324  0;
];

This system has 2 generators at bus 1 and 2 and a capacitor at bus 4.

I am also including cost of generation of reactive power from the
generators as well as the capacitors(refer mpc.gencost).

But after I 'runopf' , the opf results are the same with/without reactive
power generation cost.

results=

version: '2'
    baseMVA: 100
        bus: [5x17 double]
        gen: [2x25 double]
     branch: [7x21 double]
    gencost: [2x7 double]
      order: [1x1 struct]
         om: [1x1 opf_model]
          x: [14x1 double]
         mu: [1x1 struct]
          f: 2.0196e+03
        var: [1x1 struct]
        nln: [1x1 struct]
         et: 0.0930
    success: 1
        raw: [1x1 struct]

You can see that the gencost is only a 2x7 double. Why is the program not
taking the other rows into account?

Please help me out.
Thank you.

Reply via email to