If the isolated portions have adequate generation to operate as an island, then 
the only thing necessary is to make sure that each island has its own reference 
bus. In your case, however, I suppose there are de-energized sections. MATPOWER 
does not automatically handle the de-energized sections, so you will have to 
extract the section that is still live using extract_islands() 
<http://www.pserc.cornell.edu//matpower/docs/ref/matpower6.0b2/extract_islands.html>,
 then only run the power flow on that island.

   Ray


> On Dec 12, 2016, at 2:33 PM, Andrey Vieira <[email protected]> wrote:
> 
>  
> Good afternoon people! By performing load flow tests  in IEEE radials feeders 
> cases, 
> such as 33, 69, 84 bars, I noticed that the study does not work when I leave 
> isolated 
> sections (eg in the case 33 buses, runpf('case33'), opening section 3-23 
> causes error). Is there any
>  way in MATPOWER to perform load flow tests with isolated branches?

Reply via email to