Hi there,

if the from bus-from has a rated voltage level of 230 kV and the to-bus
of 115 kV (or vice-versa) the tap (ratio) of the transformer is 1,
because the transformer ratio equals the ratio of the defined rated
voltage levels of the buses. At least one of r or rather x shouldn't be
0, usually r!=0 and x!=0.

e.g.:
- Bus 1: 110 kV as a rated voltage level
- Bus 2: 20 kV as a rated voltage level
- Transformer from Bus 1 to Bus 2 with ur=1%, uk=10%, S=32 MVA and a
nominal ratio of 115 kV to 21 kV
- S_base = 100 MVA (used and defined in Matpower by myself)

tap or ratio = (U1n / U2n) / (U1r / U2r) = (115/21) / (110/20) = 0.9957
r = ur * S_base / S_Trafo = 0.01 * 100/32 = 0.03125 p.u.
x = sqrt(uk^2 - ur^2) * S_base / S_Trafo = sqrt(0.1^2 - 0.01^2) * 100/32
= 0.31 p.u.

Kind regards,
Chris


Am 30.12.2016 um 20:31 schrieb Angel Pastor:
>
> Dear MATPOWER community.
>
>
> Greetings and happy holidays to everyone, i have some doubts about the
> representation of the transformers, for those branches with
> transformers i put the transformation relationship betwen the voltages
> in the "from bus" and the "to bus" in the column TAP (number 9 column)
> of the branches matrix.
>
>
> In my case i have transformers of (230/115)kV, so the value i'm
> writting in the column TAP is 2, but, according to what i read this is
> valid only when r=x=0... Wich is not my case, because i have r=0 and
> x=0.075... So how can i calculate the value that should go in TAP to
> represent the transformer correctly? Should i put the performance value?
>
>
> Thank's from advance.
>