Dear All,

 

we are trying to translate the matpower casefiles to pandapower but have
encountered problems when converting cases with transformers. We would
expect transformers always to behave inductive, but the transformer branches
in the cases always seem to have a positive b value. If I am not mistaken,
that models a capacitive behaviour. An example of this can be found in
case118 with the branches that connect buses 68 (345 kV) and bus 116 (138kV)
as well as a branch that connects bus 86 (138kV) and bus 87 (161kV). Both of
these branches have a positive susceptance while connecting different
voltage levels.

 

Is there an explanation for that, i.e. do these branches not only model a
transformer but a whole substation with reactive power compensation device
as well? Or am I missing something else?

 

Thanks for your help

Leon

 

---------------------------------

 