The tap settings are provided in the case data. Look at the mpc.branch. There 
you provide all the branch data, including taps and phases of transformers.

MatPower however does not calculate the taps, if this is what you're asking. 
You must provide the taps.


________________________________
Od: [email protected] 
[[email protected]] v imenu Akash Tyagi 
[[email protected]]
Poslano: 17. maj 2017 10:44
Za: MATPOWER discussion forum
Zadeva: Re: Setting the initial values for the variables?

Hello everyone,
Is there any option in MATPOWER to set the transformer tap settings, and if it 
is then how we can set the settings and after running power flow, how these 
settings are extracted from the results?
Please help.

On Wed, May 17, 2017 at 12:10 PM, Bone, Gorazd 
<[email protected]<mailto:[email protected]>> wrote:
That's really simple. Thank you.


________________________________
Od: 
[email protected]<mailto:[email protected]>
 
[[email protected]<mailto:[email protected]>]
 v imenu Ray Zimmerman [[email protected]<mailto:[email protected]>]
Poslano: 16. maj 2017 21:10
Za: MATPOWER discussion forum
Zadeva: Re: Setting the initial values for the variables?

Since the results struct is a super-set of the input mpc, you can just use it 
directly as input.

E.g.

r1 = runpf(mpc);
r2 = runpf(r1);

When in doubt … just try it ;-)

   Ray


On May 16, 2017, at 5:58 AM, Bone, Gorazd 
<[email protected]<mailto:[email protected]>> wrote:

Hello

I wonder if it is possible to input the initial conditions of one load flow 
calculation into another load flow calculation.
In trying to develop a method that calculates the taps and phases of 
transformer, so I have to repeatedly perform Load Flow calculations one after 
another and iterate the changes in taps and phases. I believe it will be faster 
if I the results from one iteration are used as initial values in the 
concurrent iteration. I was wondering if there is a built in way to do that and 
if not, how can I do it.

Regards, Gorazd