Case B can't be solved with PQSUM, ISUM or YSUM since there are three slack 
buses. There must be only one slack (supply) bus for the distribution network.


Case A can be solved but you should put branches 1-2 and 1-3. Their parameters 
may all be zero (r, x and b). However, bear in mind the zero-impedance branches 
are problematic for the Netwon method.


Finally, do you include tie branches 5-11, 10-14 and 7-16? If yes, the network 
consists loops and can't be solved with the current version of PQSUM, ISUM or 
YSUM.


Best regards,

Mirko

On 06/29/2017 03:47 PM, Andrey Vieira wrote:

Hi All. With regard to the use of load flow for radial networks, I would
 like to know if there is for distribution systems with several separately
 represented radial feeders. That is, each one With their respective sources
 (substations).
For example, note the case 16 buses below

[cid:[email protected]]


This case can be represented in MATPOWER in two different ways, as
 below:

A)

%          bus_i     type ...


mpc.bus = [ 1          3  ...
            2          1  ...
            3          1  ...
            4          1  ...
            5          1  ...
            6          1  ...

            7          1  ...
            8          1  ...
            9          1  ...
           10          1  ...
           11          1  ...
           12          1  ...
           13          1  ...
           14          1  ...];



 B)

%          bus_i     type ...


mpc.bus = [ 1          3  ...
            2          3  ...
            3          3  ...
            4          1  ...
            5          1  ...
            6          1  ...

            7          1  ...
            8          1  ...
            9          1  ...
           10          1  ...
           11          1  ...
           12          1  ...
           13          1  ...
           14          1  ...
           15          1  ...
           16          1  ...];


When carrying out the load flow for the two cases (A and B),
success was obtained for the two cases by Newton's method.
However, for the PSUM, ISUM, and YSUM methods, none
of them were successful.
Can anyone tell me if there is the possibility of running the load flow
 for distribution systems Radials that use the representation of a
 substation for each feeder?