Vikram,

For what year is this WECC system?

Jovan


On Tue, Apr 3, 2018 at 11:54 AM, vikram reddy <[email protected]>
wrote:

> I have a 20000 bus WECC system in PSSE raw format. I am trying to run the
> DC power flow, but the total of the power injections that I got from
> MATPOWER does not equal to zero. Are the voltage angles obtained in this
> case wrong?
>
> Thanks,
> Vikram
>
> On Tue, Apr 3, 2018 at 6:46 AM, Ray Zimmerman <[email protected]> wrote:
>
>> There is no need to check. The slack bus active power will be adjusted to
>> make the injections sum to zero. And the DC power flow in MATPOWER is a
>> lossless approximation. That is, it assumes the losses are zero.
>>
>>    Ray
>>
>>
>> On Mar 28, 2018, at 2:28 PM, vikram reddy <[email protected]>
>> wrote:
>>
>> Hi,
>>
>> I am working on a 20000 bus system and running a DC load flow. Now, the
>> power injection vector computed as
>>
>>   Pbus = real(makeSbus(baseMVA, bus, gen)) - Pbusinj - bus(:, GS) /
>> baseMVA;
>>
>> In general, the total of the power injection vector should be zero
>> implying generation=load+losses. MATPOWER does not do the checking if the
>> total of injection vector is zero.
>>
>> 1. Why does MATPOWER not check if the total of injection vector goes to
>> zero? Is it not important?
>> 2.  What happens if the injection vector is not zero and running the DC
>> load flow? I assume the voltage angles thus obtained will have an error.
>> 3. Assuming losses is the total sum of Pbus vector, how should the losses
>> be distributed?
>>
>> Thanks,
>> Vikram
>>
>>
>>
>>
>