I have one confusion, on page 145 (Matpower manual for 7.0b1) in Table B-1,
it says the shunt susceptance is in MVAR , is that correct? If yes, so is
there any internal conversion for that for running power flow?

On Thu, Mar 21, 2019 at 9:09 AM Ray Zimmerman <[email protected]> wrote:

> Voltages and impedances are specified in p.u. in the case file data, but
> powers in MW and MVAr. That is, the conversion done internally, is simply
> to divide all of the powers by the baseMVA.
>
> If you were to specify the powers in p.u. and set the baseMVA to 1, you
> should get the same solution, with the solution powers also expressed in
> per-unit, of course. Internally, it would be solving everything with the
> same values.
>
>    Ray
>
> > On Mar 20, 2019, at 9:36 PM, Jubeyer Rahman <[email protected]> wrote:
> >
> > Hi,
> >
> > Is there any chance for wrong results, if I convert every
> parameters(Pg,Qg, Pmax, Qmax, etc.; every possible power flow data) that
> could be transformed into per unit and call the runpf in matpower?
> >
> > My point of confusion is, in usual case data file, only the voltages are
> given in per unit and all other parameters are usually given in actual
> units, and runpf is applied on that type of case file; is there really an
> internal conversion of the given data?
> >
> > Regards,
> > Jubeyer
>
>
>
>