Hi Prof.Ray,
     I found the mistake that I forgot to transfer the W to KW while combining 
two systems. Thanks.
Regards,
Chixin
________________________________
From: [email protected] 
<[email protected]> on behalf of 
[email protected] <[email protected]>
Sent: 02 September 2019 14:01
To: 'MATPOWER discussion forum' <[email protected]>
Subject: Power flow while involving radial systems

Dear Prof.Ray,
   The runpf and the runopf did not converge while handling a revised system 
(i.e., IEEE 30 and IEEE 33).  The revised system is attached.  Could you give 
me some suggestions when you feel convenient? Thanks.
   The revising details:  a standard IEEE 30 bus system [] is revised by 
connecting the bus 2 to the bus 1 of an IEEE 33-bus radial system [] which 
consists of 33 buses, 32 lines,  a  voltage  of  12.66kV,  load  size  of  
3.715MW  and 2.3MVar.
     In the new combined system, the original bus-index  of the IEEE 33-bus has 
increased 30 (i.e., the original bus-index 1 corresponds the new index 31, and 
so on). The resistance and reactance between bus 1 and bus 31 are 0.2030 (p.u.) 
and 0.1034 (p.u.) respectively.
Regards,
Chixin

Reply via email to