What you are describing is the complex bus power injection, not apparent power 
(which is just the magnitude of the complex power). And yes, the power in MVA 
is simply the per unit value times the MVA base (baseMVA). Kirchhoff’s current 
law (KCL) implies that all power injected into a bus (or leaving a bus) must 
sum to zero. In MATPOWER, that includes generation (Pg), load (Pd), connected 
branches (Pf), and shunts, and likewise for reactive power. So I believe your 
understanding is correct.

    Ray


On Apr 16, 2020, at 7:04 PM, yangyang 
<[email protected]<mailto:[email protected]>> wrote:

Dear Prof Ray Zimmerman,

In Matpower Technote 2,AC Power Flows, Generalized OPF Costs and their 
Derivatives using Complex Matrix Notation, we can find that bus appearant power 
is Sbus = Vbus .* conj(Ibus),where Ibus = Ybus* Vbus, and Vbus = 
Vm.*exp(Va*180/pi). But in cases, it seems that the results will be Sbus in per 
unit and it is hard to find its relationship with bus power in runpf() results. 
In my understanding, the nominal appearant power might be Sbus_nom=baseKVA.* 
Sbus, where Sbus is the appearant power in per unit mentioned above. And in 
power flow results, it should be the Pf, Pt, Qf, Qt results in branch data 
plus/subtracts (Pg -Pd) and (Qg - Qd) in bus and generator data. Is my 
understanding correct? Hoping that you can help me with it, thank you for your 
time.