In general, the line ratings RATE_A, etc, would also equal the sum of the 
individual line ratings, but in this case the capacity limit is not given 
(interpreted as unlimited) so no change.

However, a quick correction … while the total impedance (r and x) are halved, 
the total line charging (b) is doubled.

    Ray


On Apr 19, 2021, at 9:59 AM, naime ahmadi 
<[email protected]<mailto:[email protected]>> wrote:

Hello Matpower users,

I want to remove duplicate branches in IEEE 118 bus system and put an 
equivalent one. For example:
fbus tbus   r    x    b rateA rateB rateC ratio angle status angmin angmax

duplicate branches:
 42   49   0.0715 0.323 0.086 0 0 0 0 0 1 -360 360;
 42   49   0.0715 0.323 0.086 0 0 0 0 0 1 -360 360;

equivalent branch:
42 49 0.0357 0.1615 0.0430 0 0 0 0 0 1 -360 360;

Is it sufficient to only change r, x and b to equivalent one or do I need to 
have more changes?

Thanks,
Naime