If you convert everything into per-unit correctly, using a different voltage base for the different buses, it shouldn’t be a problem. I suggest finding a good textbook on converting parameters to per-unit to make sure you get it right, especially for the transformer.
Ray > On Nov 7, 2022, at 12:56 PM, Irfan Mujawar <irfanbudhg...@gmail.com> wrote: > > I want to use the MATPOWER for load flow analysis of the practical radial > distribution system. > In the system two voltage levels are there. > First is 11 kV bus (Bus 1) which is slack bus. > All other buses are of 440V bus. > There is a transformer of 11kV/440V between bus 1 and 2. > From bus 2 onwards are load bus. > At some buses load is present at some buses no load is present. > I know the values of R and X of line in ohm. > How to perform the load flow analysis of this system having two voltage > levels with transformer? > How to proceed. > > I am able to perform the load flow analysis of the system from 440V and > downstream buses i.e. with one voltage level. > I am facing the problem when I make bus 1 as slack bus with 11 kV. > > When I have added the 11 kV line and performed the load flow total losses are > less than that of load flow when only 440V line and downstream loads are > present. > > I am not getting what is wrong. > Please help. > Thank you.