The generator bus voltage for the power flow is set by the VG column of the gen 
matrix. For the OPF it is an optimization variable must remain between the 
bounds set by the VMIN and VMAX columns of the bus matrix.

You can also fix the voltages at the VG setpoint in the OPF by setting the 
opf.use_vg option to 1.

   Ray


On Jun 23, 2023, at 6:29 AM, Ігор Ткач <[email protected]> wrote:

Voltage difference of generators runpf and runopf , case9

runpf.
Bus voltages of power system and generators rigidly set to 1.04, 1.025, 1.025.
The voltage does not change during optimization.

runopf
Voltage at  generator buses after optimization 1.099, 1.097b 1.086.

Question.
Which parameter will change the voltage calculation from the generator busbar 
voltage (ronpf) that is rigidly set to the changing voltage during optimization 
(runopf)?

Igor