For shunt compensation, do we have to add the shunt compensation value at
bus 5 and 6 of bus data, and for series compensation do we have to add it
to X (column 4) of branch data? Is this the correct way?

On Thu, Nov 23, 2023 at 5:31 PM Muhammad Junaid <[email protected]>
wrote:

> Thank you so much for the detailed answer.
>
> On Wed, Nov 22, 2023 at 10:11 PM Ray Daniel Zimmerman <[email protected]>
> wrote:
>
>> Adding them to columns 3 and 4 of the bus matrix will be equivalent to
>> adding them to columns 2 and 3 of the gen matrix, assuming the bus is set
>> as a PQ bus and you are doing a simple power flow. Adding  it to bus 5 and
>> 6 of the bus matrix is *not* equivalent, since the power (as a constant
>> impedance shunt element) will depend on the voltage.
>>
>>     Ray
>>
>>
>> On Nov 17, 2023, at 11:48 PM, Muhammad Junaid <[email protected]>
>> wrote:
>>
>> Hi Sir. I hope you are doing well. If EVs are to be added as loads on
>>> buses that ave P and Q. Should the load be added in bus data or should I be
>>> added as shunt element or can it be used as negative generator?
>>
>>  You replied
>>
>>> If they are considered as fixed P and Q they can be added to any
>>> existing load in the bus matrix or they can be added as a negative
>>> generator. If you add it as a shunt (in the bus matrix) it will be treated
>>> as a constant impedance element.
>>
>>  If we use Distributed Generators to inject
>>
>>    - Active Power Only
>>    - Reactive Power Only
>>    - Active and Reactive both
>>    - Active but absorb Reactive Power
>>
>> Can the active and reactive power be added to Column 5 and 6 of {Bus
>> Data Format
>>
>>        1   bus number (positive integer)
>>        2   bus type
>>                PQ bus          = 1
>>                PV bus          = 2
>>                reference bus   = 3
>>                isolated bus    = 4
>>        3   Pd, real power demand (MW)
>>        4   Qd, reactive power demand (MVAr)
>>        5   Gs, shunt conductance (MW demanded at V = 1.0 p.u.)
>>        6   Bs, shunt susceptance (MVAr injected at V = 1.0 p.u.)
>>        7   area number, (positive integer)
>>        8   Vm, voltage magnitude (p.u.)
>>        9   Va, voltage angle (degrees)
>>    (-)     (bus name)
>>        10  baseKV, base voltage (kV)
>>        11  zone, loss zone (positive integer)
>>    (+) 12  maxVm, maximum voltage magnitude (p.u.)
>>    (+) 13  minVm, minimum voltage magnitude (p.u.)
>>
>> }
>> or they should be added in columns 2 and 3 of the Generator Data Format?
>> or Will they have the same effect? Thanks
>>
>>
>>

Reply via email to