I finally got a chance to have a look at this case, and I’m afraid I don’t
understand the source of the large voltage angle differences between the 132 kV
buses and the other buses in your attached load flow report, unless the
connection transformers are phase-shifting transformers, in which case you
would need to introduce the corresponding phase shift in the SHIFT column (10)
of the corresponding rows of the branch matrix.
Hope this helps,
Ray
On Nov 10, 2024, at 11:32 PM, Mohammed Alhajri <[email protected]> wrote:
Dear Team,
When running the power flow analysis on the attached model, I am working to
achieve results identical to those in the attached load flow report. While the
voltage magnitudes and angles across most buses are close to the desired
values, I am seeing an approximate 150 degree phase shift at the 132kV buses
between my results and the expected load flow output.
Could you advise on how to adjust or correct this phase shift issue to align my
results with the desired load flow for the 132kV buses? Any guidance on
parameter settings or adjustments would be greatly appreciated.
Thank you in advance for your support.
Best regards,
Mohammed.