David:

One may use the AC voltage polarity to detect the current direction (in or
out) of the motor to determine if working as a motor ( IN) or as a generator
(OUT).

Also, one needs to determine the current phase angle to fully defining the
motor operation
Of  course the Synchronous detection will show such phase angle
 -- This is not for the novice -- 

To see the effect of synchronous detection assume that you have 2 voltages,
one called Motor and another Generator, inter-connected with a resistor in
series ( The clamp meter).
Make Generator voltage 2 X, the Motor Voltage, so the current will flow from
Generator to Motor.
Make Motor Voltage 2 X the Generator Voltage, so the current will flow from
Motor to Generator

The clamp meter just measures the current out of the generator, without any
phase angle determination.

I hope this helps, if not ask again

Nando


----- Original Message ----- 
From: "David Green" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, May 09, 2005 12:18 PM
Subject: Re: [microhydro] Digest Number 1153


> Hi Nando,
>
> Could you expound a bit on the "(synchronous current detection)" that you
> mention.  I use a clamp on meter as an amperage detector.  As I change
> nozzle configuration on a pelton I can see my Kw's.
>
> David
> ----- Original Message ----- 
> From: "Nando" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Friday, May 06, 2005 5:23 AM
> Subject: Re: [microhydro] Digest Number 1153
>
>
> > Perran:
> >
> > The induction motor (Generator) GRID connected, follows the GRID
frequency
> > and the RPM of the GEN, in this case, is going to be the RPM defined by
> > the
> > number of poles and the GRID frequency PLUS twice the SLIP Value.
> > To detect this you may have an RPM detector to make sure that the GEN
does
> > not run as a motor, which happens if the hydro pressure lowers.
> > Also, techniques like reading the current into the grid with the voltage
> > as
> > a reference to detect the current direction -- this is faster and more
> > accurate.(synchronous current detection).
> >
> > Frequency will not move from the GRID frequency-- it can  not  move (
> > vary)
> > because the motor bias is set by the GRID.
> >
> > If the generator has excessive applied torque ( by the Turbine), one may
> > have issues like heavy currents and  (PF) Power Factor.
> >
> > And for those interested, one may have two hydros operating in parallel,
> > in
> > where one is a master (GRID) and the other is the slave ( in this case
an
> > induction motor) which should be capable of producing not more that
about
> > 50
> > % of the master.
> >
> > Regards
> >
> > Nando
> >
> >
> >
> > ----- Original Message ----- 
> > From: "H2MJD" <[EMAIL PROTECTED]>
> > To: <[email protected]>
> > Sent: Thursday, May 05, 2005 8:48 PM
> > Subject: Re: [microhydro] Digest Number 1153
> >
> >
> >>
> >> Can someone tell me how you can provide this 'utility required'
> >> protection
> >> with a directly connected induction motor. My understanding is that
power
> > will
> >> flow into or out of the grid in a seemless manner depending only on the
> > speed
> >> of the motor/generator shaft and the torque applied. Am I right ??
> >>
> >> Perran Newman
> >>
> >>
> >>
> >> Perran,
> >> You are right. When wiring in the motor/generator typically a magnetic
> > contactor (motor starter) is used to apply power to the unit. The
> > Over/under
> > voltage and over/under freq relays monitor the voltage and frequency of
> > the
> > utility power. If the voltage or freq move outside the utility
perscribed
> > limits(and this will only happen if the utility is experiencing a
problem)
> > these relays will remove power from the magnetic contactor's coil and
the
> > motor/gen will then be isolated from the utility grid thereby providing
> > safety to all.......i hope this helps.......mark
> >>
> >>
> >>
> >>
> >>
> >>
> >> [Non-text portions of this message have been removed]
> >>
> >>
> >>
> >>
> >>
> >>
> >> Does your company feature in the microhydro business directory at
> > http://microhydropower.net/directory ? If not, please register free of
> > charge and be exposed to the microhydro community world wide!
> >>
> >> NOTE: The advertisements in this email are added by Yahoogroups who
> > provides us with free email group services. The microhydro-group does
not
> > endorse products or support the advertisements in any way.
> >>
> >> More information on micro hydropower at http://microhydropower.net
> >>
> >> To unsubscribe: send empty message to
> > [EMAIL PROTECTED]
> >> Yahoo! Groups Links
> >>
> >>
> >>
> >>
> >>
> >>
> >
> >
> >
> >
> >
> >
> > Does your company feature in the microhydro business directory at
> > http://microhydropower.net/directory ? If not, please register free of
> > charge and be exposed to the microhydro community world wide!
> >
> > NOTE: The advertisements in this email are added by Yahoogroups who
> > provides us with free email group services. The microhydro-group does
not
> > endorse products or support the advertisements in any way.
> >
> > More information on micro hydropower at http://microhydropower.net
> >
> > To unsubscribe: send empty message to
> > [EMAIL PROTECTED]
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
> >
> >
> >
>
>
>
>
>
>
> Does your company feature in the microhydro business directory at
http://microhydropower.net/directory ? If not, please register free of
charge and be exposed to the microhydro community world wide!
>
> NOTE: The advertisements in this email are added by Yahoogroups who
provides us with free email group services. The microhydro-group does not
endorse products or support the advertisements in any way.
>
> More information on micro hydropower at http://microhydropower.net
>
> To unsubscribe: send empty message to
[EMAIL PROTECTED]
> Yahoo! Groups Links
>
>
>
>
>
>





------------------------ Yahoo! Groups Sponsor --------------------~--> 
What would our lives be like without music, dance, and theater?
Donate or volunteer in the arts today at Network for Good!
http://us.click.yahoo.com/TzSHvD/SOnJAA/79vVAA/FGYolB/TM
--------------------------------------------------------------------~-> 

Does your company feature in the microhydro business directory at 
http://microhydropower.net/directory ? If not, please register free of charge 
and be exposed to the microhydro community world wide!

NOTE: The advertisements in this email are added by Yahoogroups who provides us 
with free email group services. The microhydro-group does not endorse products 
or support the advertisements in any way. 

More information on micro hydropower at http://microhydropower.net

To unsubscribe: send empty message to [EMAIL PROTECTED] 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/microhydro/

<*> To unsubscribe from this group, send an email to:
    [EMAIL PROTECTED]

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/
 


Reply via email to