Unnamed Administration sources reported that Crist J. Clark said:
> 
> 
> On Sun, Oct 20, 2002 at 12:22:50 -0400, Howard C. Berkowitz wrote,
> > 3. Consider putting data centers not in the ground floor on the basement,
> >     but not too high either.  Sean, I believe, knows the specific NFPA rule,
> >     but IIRC you can't have a UPS with acid electrolyte above the third floor.
> >     So, you can put a data center on the 2nd floor and both allow the UPS
> >     and have a place for the water to drain.
> 
> This is not at all my area of expertise, but I'm curious, why does
> does the UPS need to be on the same floor with the data center racks
> at all?

Welll... "need"????

Issues include: buildings tend to rent by the floor, and various
FD regs govern penetrations and safety cutoffs. 

But if those are solvable; real pluses are you can use low-grade
"core" space for both, with better floor loading. (Many buildings
are like WTC -- the support is in the center, everything out of
that is "hung" out there.) 

And you segregate the machines from the fumes... ALWAYS a
good idea.





-- 
A host is a host from coast to [EMAIL PROTECTED]
& no one will talk to a host that's close........[v].(301) 56-LINUX
Unless the host (that isn't close).........................pob 1433
is busy, hung or dead....................................20915-1433

Reply via email to