We use Intermapper, an SNMP network monitoring system, which supports UNIX 
scripting. Intermapper probes two Weathergoose temperature sensors, and calls a 
script with the values it retrieves. When both sensors exceed a certain 
threshold, the script sends an snmp relay trip signal to the Weathergoosen, 
which close a pair of dry contacts wired in series to the emergency power off 
contacts for the whole-room UPS.

We chose to use two sensors and two dry contact relays to protect against false 
trips, and thus false shut downs. Before the trigger temperature is reached, 
the NMS would have sent various escalating alarms to on call staffers, who 
hopefully would intervene before this point. This protection is for the worst 
case scenario where nobody responds and the equipment is at risk of damage.

We could have commanded an orderly shut down to all servers, but decided that 
it would be better to kill the power in the event of a runaway heat vent than 
to try to make it through all the disk activity necessary for a clean shut down.

This system has triggered one time, successfully shutting down the data center 
on a holiday weekend when people missed their notifications, and undoubtedly 
saved a lot of hard drives. When we got to the room the temperature was over 
115°, but the power was cut at 95°.

 -mel

On May 27, 2019, at 11:01 AM, Dovid Bender 
<[email protected]<mailto:[email protected]>> wrote:

Hi,

Is anyone aware of a device that will cut the power if the room goes above X 
degrees? I am looking for something as a just in case.


Regards,

Dovid

Reply via email to