Yes, most grounding out now that utilities do for work is all phases to one 
another, to the neutral and to the ground.

From: NANOG <nanog-bounces+john=vanoppen....@nanog.org> On Behalf Of Mel Beckman
Sent: Monday, August 30, 2021 10:59 AM
To: Aaron C. de Bruyn <aa...@heyaaron.com>
Cc: NANOG Operators' Group <nanog@nanog.org>
Subject: Re: Reminder: Never connect a generator to home wiring without 
transfer switch

Aaron,

Your incorrect assumption is that lineman are tying phases to earth ground, a 
discontinued practice that killed many lineman up through 1980, despite its 
seeming faultless logic.

The current safety practice is called “equipotential grounding”, which doesn’t 
go to earth. Thus an backed can change the balance of potentials, resulting in 
lethal currents. As other have pointed out with real-word examples, this is a 
major safety issue, cause by the many “dumb enough” DIYers out there.

All explained elsewhere in the thread. I recommend you review the previous 
discussion, to avoid creating a NANOG bridge loop :)

 -mel

On Aug 30, 2021, at 9:43 AM, Aaron C. de Bruyn 
<aa...@heyaaron.com<mailto:aa...@heyaaron.com>> wrote:

I've been following the thread.
If I'm dumb enough to back feed through the transformer into the downstream 
side of the downed line, how is it going to be a problem if linemen are 
grounding the phases on *both sides* of the work area.
That's what Ben seemed to be implying.