> On Wed, 27 May 2009, Seth Mattinen wrote: > > > Here's the L-G voltage off the 208v taps from an isolation transformer in a > > system with no neutral: http://ninjamonkey.us/not_120_volts.jpg > > Not 120, but 90 give or take. 90 is at the low end of the acceptable > range for common household 110/120v service.
Yeah, but that's L-G voltage (geez, did you even look at the picture?) And Seth just finished telling us that it was 211 L-L: Seth > "The L-L voltage on that same PDU is 211." What's going to be presented at the neutral and hot of the 5-15R of the monitor power adapter are the L and L. Think about it. Or get out a meter and test. > Depending on how the phases are balanced in your facility, you may see > that fluctuate up or down, of course. If you measure hot to hot on the > same PDU, do you get anywhere close to 208? Yes, Seth just finished telling us that in the portion of his message you conveniently snipped. > I'm going to suspect either > your fairly out of balance, or you've got a good bit of voltage drop by > the time it arrives.... > > But since the concensus from those who haven't used this is that the > device will present 208/240 at the 5-15 plug, I withdraw my suggestion and > leave you to your own methods. (for the rest, test it yourself) For those of us who *have* used this, we're telling you that it'll present 208/240 at the 5-15R. > I also won't argue using ground for neutral, that's like arguing bonded vs > unbonded panels. No it's not. Only idiots argue for using ground for neutral. In doubt? Ask your electrical inspector. ... JG -- Joe Greco - sol.net Network Services - Milwaukee, WI - http://www.sol.net "We call it the 'one bite at the apple' rule. Give me one chance [and] then I won't contact you again." - Direct Marketing Ass'n position on e-mail spam(CNN) With 24 million small businesses in the US alone, that's way too many apples.