On Thursday, December 02, 2010 12:51:42 pm Kevin Day wrote:
> For standard 110V service, you use a single-wide breaker and send one hot 
> phase + neutral and you get 110V. The difference between two phases is 208 
> volts though, so you use a double wide breaker and can send to device without 
> using a neutral wire. Just 2 hots and a ground. If that's all you're doing 
> (you don't need legacy 110V service anywhere) you skip the ground wire going 
> into the panel entirely.

The photo of the Square-D QO plugin breaker panel was nice; thanks.  Our 
Liebert 'precision power' PDU's have what appear to be GE panelboards on the 
120/208 side, 42 position, two panelboards per PDU. They are wired like the 
Square-D in you picture.

However, there is one thing in your reply that needs clarification.  A wye 
connected branch circuit panelboard must always be equipped with a grounded 
conductor (neutral) AND a grounding conductor (ground) to meet code.  That is 
unless the panel is listed for delta use in a 'neutral-less' arrangement and no 
single-pole breakers are present in the panel.  The grounding conductor must 
never be used as the grounded conductor; the ground is only for fault currents, 
never for load currents, and the grounded conductor must be bonded to the 
grounding conductor only at the service disconnect.  

That's in a simple single grounding conductor system; many datacenters are 
wired with separate safety and signal grounding conductors (ours is) that 
require special precautions to be taken.  The signal ground is often called the 
technical ground in the industry, and is, per NEC, always bonded to the safety 
(or NEC) ground at the service disconnect.  That makes it real fun.

Reply via email to