Of our three datacenters, this is what we saw:

Parsippany 1 (OCT) - The worst we saw here was several sub-second power hits. 
UPS's held without problem, and we did not transfer to generator at all yet.

Parsippany 2 (WBR) - Transferred to generator at about 7:55 PM EST Monday as a 
precautionary measure due to ongoing utility power hits. However, shortly after 
transfer, utility voltage went to 0 on all phases; around 10p power returned, 
but abnormally high (seeing about 550 volts on 480 volt bus). We retransferred 
last night as utility voltage settled down.

Cedar Knolls 1 (MMU) - Briefly transferred to generator around 7:10, then back 
to utility. We then force transferred to generator around 8pm and stayed until 
this morning. Returned to utility and all systems are normal.

I would be interested to know how the power outages due to the storm have negatively affected air pollution and the smog problem in the area. Due to generators burning huge amounts of diesel, generators which undoubtedly have no meaningful air pollution control to speak of.

http://www.nytimes.com/2012/09/23/technology/data-centers-waste-vast-amounts-of-energy-belying-industry-image.html?pagewanted=all&_r=0

"Most data centers, by design, consume vast amounts of energy in an incongruously wasteful manner, interviews and documents show. Online companies typically run their facilities at maximum capacity around the clock, whatever the demand. As a result, data centers can waste 90 percent or more of the electricity they pull off the grid, The Times found.

To guard against a power failure, they further rely on banks of generators that emit diesel exhaust. The pollution from data centers has increasingly been cited by the authorities for violating clean air regulations, documents show. In Silicon Valley, many data centers appear on the state government’s Toxic Air Contaminant Inventory, a roster of the area’s top stationary diesel polluters."


Greetings,
Jeroen

--