Another option is an above ground  cabinet.  Many telecoms use them.

Thomas L Graves
Sent from my IPhone 


> On Nov 13, 2013, at 8:04 PM, "Justin M. Streiner" <[email protected]> 
> wrote:
> 
>> On Wed, 13 Nov 2013, Roy Hockett wrote:
>> 
>> Thank you for comments. Let me clarify the situation.  We have a building 
>> that has been fiber cross connect
>> location and is being demolished.  This location has about 20 fiber cable 
>> entering where we patch between
>> fiber paths.  If we relocated these cross connect field to another building 
>> and that build is demolished we have
>> to do this all over again, so the desire was to have an independent facility 
>> for the fiber cross connect field, but
>> I am guessing due to esthetics the below ground vault was selected, we just 
>> learned of this selection and thus
>> my query to this group to find other that have dealt with similar situations 
>> and if so, experience base recommendations,
>> and things to be aware of.
> 
> If the vault has a controlled environment and access, similar to what you 
> would find inside of a comms room, that's one thing.  If it's more like a 
> typical manhole (damp, dirty, dark, possible temperature extremes, other 
> utilities/hazards), then the only thing that should be in there is a 
> water-tight splice case.  Fiber patches need to be in a clean environment.
> 
> Did this project provide any funds for relocation or replacement of the 
> communications facilities that would be lost due to the demolition?  We've 
> gone through this many times on our campus.
> 
> jms
> 