----- Original Message -----
> From: "Seth Mattinen" <[email protected]>

> On 3/19/14, 10:21, Jay Ashworth wrote:
> > It is exactly that: no one says you*can't* wire a 20A branch circuit
> > with #10.
> >
> > It is even*possible*, though unlikely, that if you did so, you wouldn't
> > have to derate it to 80%. I would have to reread the Code to be sure.
> 
> Well, I'd say it's pretty likely. However highly unlikely to be
> code-worthy of slapping on a 30A breaker in place of a 20.

Well, the situation were were discussing was replacing

30A CB <--> 10 AWG <--> L6-30

with 

20A CB <--> 10 AWG <--> L6-20

and as I was reminded, you'd still have to derate that unless the
CB was magnetic.  And you can't leave the breaker at 30, cause then the 
attached 20A single device isn't protected properly by it.

So I was worng on the derating.

Cheers,
-- jra

-- 
Jay R. Ashworth                  Baylink                       [email protected]
Designer                     The Things I Think                       RFC 2100
Ashworth & Associates       http://www.bcp38.info          2000 Land Rover DII
St Petersburg FL USA      BCP38: Ask For It By Name!           +1 727 647 1274

Reply via email to