We would typically order a 20 or 30-amp 208v circuit per rack for a flat fee 
then install a metered PDU to make sure we didn’t overload it.  The flat fee 
per-circuit seems pretty standard in the US.  Using your own metered PDU would 
help predict the usage if you’re being billed by kWH.

Kenny

From: NANOG <[email protected]> On Behalf Of Baldur Norddahl
Sent: Thursday, September 20, 2018 11:34 PM
To: [email protected]
Subject: Re: overages for power usage

The fuses might match what you ordered. If you go over you might lose power due 
to a blown fuse.

When there is A and B power for redundancy, you need to make sure that one side 
can take the whole load without blowing any fuses. Otherwise you have no 
redundancy.

Regards

Baldur


fre. 21. sep. 2018 04.12 skrev Alan Hannan 
<[email protected]<mailto:[email protected]>>:
What kind of typical overage costs have you seen when a customer/you use more 
than you've committed to?

I'm especially interested in datacenter power situations, where maybe you sign 
up for 5kw or 500kw and use more than that in a given month.  Is it billed at 
the same rate?  Is it billed at a higher rate?  What's the % increase of the 
higher rate versus the regular rate?

Thanks!