Former employer was in Expedient’s DC. You can honestly do better than 
Expedient. Look into the Power Redundancy, Cooling Efficiency of the building, 
if the site is a purpose built DC (Expedient in Cleveland is not). Is Cloud 
Connect for backups important? Have you identified your requirements? If you 
need a starting point look at the following: Data Center Certification (from 
the Uptime Institute), Distance, Compliance (if needed), Level of Controlled 
Access, Power SLA, N+1 Cooling, Multi-Homed ISPs, Uptime %, Monitoring, NOC, 
Purpose Built DC.

Involta has a really good data center in Independence, Akron, and a very 
impressive site near Pittsburgh. They would give you the option of having 
Hot/Hot datacenters with their connectivity. I’m not sure if you have to be in 
Cleveland or Cincinnati, but Cyxtera has an AMAZING data center in Columbus. 
(The DC can withstand winds up 140 MPH, is on the Century Link backbone, and 
has a solid rubber roof with no holes or cooling systems on the roof.)

Thank you,

David Kehoe

From: NANOG <[email protected]> On Behalf Of [email protected]
Sent: Friday, January 4, 2019 7:00 AM
To: [email protected]
Subject: NANOG Digest, Vol 132, Issue 4

Send NANOG mailing list submissions to
[email protected]<mailto:[email protected]>

To subscribe or unsubscribe via the World Wide Web, visit
https://mailman.nanog.org/mailman/listinfo/nanog<https://mailman.nanog.org/mailman/listinfo/nanog>
or, via email, send a message with subject or body 'help' to
[email protected]<mailto:[email protected]>

You can reach the person managing the list at
[email protected]<mailto:[email protected]>

When replying, please edit your Subject line so it is more specific
than "Re: Contents of NANOG digest..."


Today's Topics:

1. Re: Cleveland/Cincinnati Co-location
(Allen McKinley Kitchen (gmail))
2. Re: Service Provider NetFlow Collectors (Aaron)
3. Re: Cleveland/Cincinnati Co-location (Shawn Ritchie)
4. Re: Announcing Peering-LAN prefixes to customers (Andy Davidson)
5. Report on Legal Barriers to RPKI Adoption (Christopher S. Yoo)
6. 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 286, 3320, 
5511, 6461,
6762, 6830, 8220, 9002, 12956 (Dominik Bay)
7. Re: 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 286, 
3320, 5511,
6461, 6762, 6830, 8220, 9002, 12956 (Jeff Shultz)
8. Astronaut accidently calls 911 from space (Sean Donelan)
9. Re: Cellular backup connections (Dovid Bender)
10. Re: 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 286, 
3320, 5511,
6461, 6762, 6830, 8220, 9002, 12956 (Job Snijders)


----------------------------------------------------------------------

Message: 1
Date: Thu, 3 Jan 2019 10:50:45 -0500
From: "Allen McKinley Kitchen (gmail)"
<[email protected]<mailto:[email protected]>>
To: "Justin M. Streiner" <[email protected]<mailto:[email protected]>>
Cc: NANOG <[email protected]<mailto:[email protected]>>
Subject: Re: Cleveland/Cincinnati Co-location
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset=us-ascii

+1 for Expedient. Not a current customer but a VERY satisfied former customer. 
(Decision to leave them was a foul case of penny-pincher mismanagement, above 
my pay grade and over my objections.)

..Allen

> On Jan 3, 2019, at 01:00, Justin M. Streiner 
> <[email protected]<mailto:[email protected]>> wrote:
>
>> On Tue, 1 Jan 2019, Mitchell Lewis wrote:
>>
>> I am working on project that may involve building points of presence in 
>> Cleveland & Cincinnati. Any suggestions as to which colocation facility in 
>> each city to build in? The prime factor of consideration for this project is 
>> access to waves to places like Chicago, New York & Ashburn. It would be nice 
>> to have multiple wave provider options to choose from.
>>
>> I have been looking at Cyrus One-7thStreet in Cincinnati & Databank in 
>> Cleveland.
>
> Expedient has two facilities in Cleveland that might be worth looking at.
>
> Thank you
> jms


------------------------------

Message: 2
Date: Thu, 3 Jan 2019 10:40:44 +0900
From: Aaron <[email protected]<mailto:[email protected]>>
To: "Michel 'ic' Luczak" <[email protected]<mailto:[email protected]>>
Cc: Erik Sundberg <[email protected]<mailto:[email protected]>>, 
"[email protected]<mailto:[email protected]>"
<[email protected]<mailto:[email protected]>>
Subject: Re: Service Provider NetFlow Collectors
Message-ID:
<cabq4n+trepexpgwjjrdgrjzsulbhvpo9ped5mxz+vn7p122...@mail.gmail.com<mailto:cabq4n+trepexpgwjjrdgrjzsulbhvpo9ped5mxz+vn7p122...@mail.gmail.com>>
Content-Type: text/plain; charset="utf-8"

Throwing my hat in the ring also (vendor from fmadio)
https://github.com/fmadio/pcap2json<https://github.com/fmadio/pcap2json>

Not exactly a newflow collector, its pcap -> flowgen -> elk on a single
box, working very well so far, still work in progress.

Problem with logstash is its too slow for high flow rates. So we did
everything inside the flow generator for direct ELK bulk uploads removing
logstash completely.

Cheers
Aaron

On Mon, 31 Dec 2018 at 18:40, Michel 'ic' Luczak 
<[email protected]<mailto:[email protected]>> wrote:

> Don’t underestimate good old ELK
> https://www.elastic.co/guide/en/logstash/current/netflow-module.html<https://www.elastic.co/guide/en/logstash/current/netflow-module.html>
> + 
> https://github.com/robcowart/elastiflow<https://github.com/robcowart/elastiflow>
>
> BR, ic
>
> On 31 Dec 2018, at 04:29, Erik Sundberg 
> <[email protected]<mailto:[email protected]>> wrote:
>
> Hi Nanog….
>
> We are looking at replacing our Netflow collector. I am wonder what other
> service providers are using to collect netflow data off their Core and Edge
> Routers. Pros/Cons… What to watch out for any info would help.
>
> We are mainly looking to analyze the netflow data. Bonus if it does ddos
> detection and mitigation.
>
> We are looking at
> ManageEngine Netflow Analyzer
> PRTG
> Plixer – Scrutinizer
> PeakFlow
> Kentik
> Solarwinds NTA
>
>
> Thanks in advance…
>
> Erik
>
>
> ------------------------------
>
> CONFIDENTIALITY NOTICE: This e-mail transmission, and any documents, files
> or previous e-mail messages attached to it may contain confidential
> information that is legally privileged. If you are not the intended
> recipient, or a person responsible for delivering it to the intended
> recipient, you are hereby notified that any disclosure, copying,
> distribution or use of any of the information contained in or attached to
> this transmission is STRICTLY PROHIBITED. If you have received this
> transmission in error please notify the sender immediately by replying to
> this e-mail. You must destroy the original transmission and its attachments
> without reading or saving in any manner. Thank you.
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/2975478b/attachment-0001.html<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/2975478b/attachment-0001.html>>

------------------------------

Message: 3
Date: Thu, 3 Jan 2019 11:21:32 -0600
From: Shawn Ritchie <[email protected]<mailto:[email protected]>>
To: "Allen McKinley Kitchen (gmail)" 
<[email protected]<mailto:[email protected]>>
Cc: "Justin M. Streiner" <[email protected]<mailto:[email protected]>>, 
NANOG
<[email protected]<mailto:[email protected]>>
Subject: Re: Cleveland/Cincinnati Co-location
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset=utf-8

On Jan 3, 2019, at 9:50 AM, Allen McKinley Kitchen (gmail) 
<[email protected]<mailto:[email protected]>> wrote:
>
> +1 for Expedient. Not a current customer but a VERY satisfied former 
> customer. (Decision to leave them was a foul case of penny-pincher 
> mismanagement, above my pay grade and over my objections.)
>
> ..Allen
>
>> On Jan 3, 2019, at 01:00, Justin M. Streiner 
>> <[email protected]<mailto:[email protected]>> wrote:
>>
>>> On Tue, 1 Jan 2019, Mitchell Lewis wrote:
>>>
>>> I am working on project that may involve building points of presence in 
>>> Cleveland & Cincinnati. Any suggestions as to which colocation facility in 
>>> each city to build in? The prime factor of consideration for this project 
>>> is access to waves to places like Chicago, New York & Ashburn. It would be 
>>> nice to have multiple wave provider options to choose from.
>>>
>>> I have been looking at Cyrus One-7thStreet in Cincinnati & Databank in 
>>> Cleveland.
>>
>> Expedient has two facilities in Cleveland that might be worth looking at.
>>
>> Thank you
>> jms

I’m in Expedient’s Cleveland DC and will second that they’re decent.

—
Shawn

------------------------------

Message: 4
Date: Thu, 3 Jan 2019 20:08:46 +0000
From: Andy Davidson <[email protected]<mailto:[email protected]>>
To: Dominic Schallert <[email protected]<mailto:[email protected]>>
Cc: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>
Subject: Re: Announcing Peering-LAN prefixes to customers
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="utf-8"

Hi, Dominic --

On 20/12/2018, 17:49, Dominic Schallert 
<[email protected]<mailto:[email protected]>> wrote:

> this might be a stupid question but today I was discussing with a colleague if
> Peering-LAN prefixes should be re-distributed/announced to direct 
> customers/peers.
> My standpoint is that in any case, Peering-LAN prefixes should be filtered 
> and not
> announced to peers/customers because a Peering-LAN represents some sort of
> DMZ and there is simply no need for them to be reachable by third-parties not 
> being
> physically connected to an IXP themselves.

There are no stupid questions! It is a good idea to not BGP announce and 
perhaps also to drop traffic toward peering LAN prefixes at customer-borders, 
this was already well discussed in the thread. But there wasn’t a discussion on 
how we got to this point. Until the Cloudflare 2013 BGP speaker attack, that 
sought to flood Cloudflare’s transfer networks and exchange connectivity (and 
with it saturating IXP inter-switch links and IXP participant ports), it was 
common for IXP IPv4/6 peering LANs to be internet reachable and BGP transited.

This facilitated troubleshooting (e.g. traceroutes showing peering lan 
interfaces in traceroutes instead of ‘starring out’) and PMTUD (e.g. see 
recommendation in 
https://www.ripe.net/ripe/mail/archives/ipv6-wg/2011-July/001839.html<https://www.ripe.net/ripe/mail/archives/ipv6-wg/2011-July/001839.html>
 which actually asked for IXP peering LANs to be announced).

There are good reasons to announce but there are better reasons to filter. The 
security benefits of filtering outweigh the upsides on today’s internet, but 
fashions and best practice may further evolve over time.

Andy


--
Andy Davidson
Director, Asteroid International BV 
www.asteroidhq.com<http://www.asteroidhq.com>
Director, Euro-IX - The European Internet Exchange Association 
www.euro-ix.net<http://www.euro-ix.net>



------------------------------

Message: 5
Date: Thu, 3 Jan 2019 20:51:56 +0000
From: "Christopher S. Yoo" <[email protected]<mailto:[email protected]>>
To: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>
Cc: David Wishnick <[email protected]<mailto:[email protected]>>
Subject: Report on Legal Barriers to RPKI Adoption
Message-ID:
<byapr01mb4936273f035e0be12eb3dcd8fd...@byapr01mb4936.prod.exchangelabs.com<mailto:byapr01mb4936273f035e0be12eb3dcd8fd...@byapr01mb4936.prod.exchangelabs.com>>

Content-Type: text/plain; charset="utf-8"

As many of you know, the prospects for widespread RPKI adoption grew more 
promising in 2018. Cloudflare issued route origin authorizations ("ROAs") to 
cover 25% of its prefixes, including its 1.1.1.1<http://1.1.1.1> resolver and 
DNS servers. NTT began treating RPKI ROAs as if they were IRR route(6)-objects. 
Google announced its intention to begin filtering routes in early 2019. The 
Mutually Agreed Norms for Routing Security now has over 100 network operators 
signed on.

Still, as 2019 begins, many worry that legal issues are hindering RPKI 
adoption. This is especially true for North American networks, which have a 
comparatively low percentage of IPv4 space covered by ROAs, and whose ROAs are 
comparatively underutilized by parties using RPKI-based route origin validation 
("ROV") to inform their routing decisions.

My coauthor (David Wishnick) and I have spent the past year delving into the 
legal issues surrounding RPKI. Today, we are publicizing our report on how the 
network operator community should address these issues. It is available 
here<https://ssrn.com/abstract=3308619<https://ssrn.com/abstract=3308619>>. If 
you are interested in the future of routing security, we encourage you to read 
it (or its Executive Summary). We've tried to keep the legalese to a minimum.

RPKI was a major topic of discussion at NANOG 74 and ARIN 42 in Vancouver. 
Going forward, we expect to continue a fruitful dialogue about how the network 
operator community can reduce the legal barriers to RPKI adoption.

Here is a summary of our recommendations:

On the ROV side of the equation, the principal legal hindrances have to do with 
the terms and conditions governing access to the RPKI repository offered by 
ARIN in its Relying Party Agreement ("RPA"), and in the manner it has employed 
to ensure the agreement is binding. Regarding ROV:

1. The goal of widespread ROV counsels in favor of ARIN reviewing its current 
approach to repository distribution, embodied in the RPA. We conclude that two 
paths would be reasonable. First, ARIN should consider dropping the RPA 
altogether. This would remove the most significant legal barriers to widespread 
utilization of the ARIN RPKI repository. Second, because the legal risks faced 
by ARIN in an RPA-free world are ultimately uncertain, it would also be 
reasonable for ARIN to maintain the RPA for the purposes of contractually 
allocating risks to the parties best positioned to reduce and mitigate them. If 
ARIN keeps the RPA, ARIN should consider removing the RPA's indemnification 
clause, instead relying solely on the RPA's disclaimers of warranties and 
limitations of liability, or at least reducing the indemnification clause's 
scope to eliminate the problem of moral hazard.

2. Developers of RPKI validation software should consider integrating 
acceptance of ARIN's RPA into their software workflows. ARIN recently enabled 
this possibility, and developers should deliberate on whether to capitalize on 
the opportunity.

3. The network operator community and ARIN should broadly publicize ARIN's 
policy of revising various RPA clauses for government entities that are 
prohibited from agreeing to them.

4. In addition to the important step ARIN has already taken to enable 
third-party software developers to integrate RPA acceptance into their software 
workflows, ARIN should consider reducing the barriers to third-party service 
development imposed by the RPA's prohibited conduct clause. Specifically, ARIN 
should consider methods for allowing approved developers to make use of RPKI 
information as an input into more sophisticated services.

5. Separately, ARIN should consider revising the prohibited conduct clause to 
allow broader distribution of information created with RPKI as an input for 
research and analysis purposes.

6. As a general alternative, the Internet community should consider whether to 
develop a separate corporate entity that would be responsible for operational 
aspects of RPKI repository provision. That corporation could conduct such 
activities for the North American region, or on a worldwide basis.

Regarding the ROA-issuance side of the equation, the principal legal obstacles 
stem from the terms and conditions found in ARIN's Registration Services 
Agreement ("RSA"), Legacy Registration Services Agreement ("LRSA"), and RPKI 
Terms of Service. Regarding these, the report recommends the following:

1. ARIN should consider adopting a pathway to provide RPKI services that would 
explicitly refrain from altering the existing balance of property and 
transferability rights associated with IP address allocations.

2. The network operator community and ARIN should broadly publicize ARIN's 
policy of revising certain RSA/LRSA and RPKI Terms of Service clauses for 
government entities that are prohibited from agreeing to them. ARIN should also 
begin presenting the RPKI Terms of Service to newly-onboarded members alongside 
their RSA/LRSA, so that organizations spend less time dealing with legal issues 
overall.

Separately, the report recommends that the network operator community consider 
whether to encourage companies and the federal government to include RPKI 
adoption in procurement best practices or requirements.

In tandem with recommendations designed to encourage adoption, the report also 
makes two recommendations concerning operational readiness for widespread RPKI 
deployment. Specifically:

1. To reduce any legal risks associated with RPKI, the network operator 
community should focus on adopting operational best practices. No system is 
100% reliable across all contingencies; as a result, operators should prepare 
for outages and other headaches. RPKI implementations should be resilient in 
the face of such contingencies.

2. The five RIRs should work to ensure readiness for widespread RPKI adoption 
and strive to publicize deeper details on their service-level intentions to the 
Internet community.

This research is supported by NSF Award No. 1748362. The contents of the report 
represent our independent views, not those of the NSF. Any mistakes, of course, 
are also ours alone.


Christopher S. Yoo
John H. Chestnut Professor of Law, Communication, and Computer & Information 
Science
Founding Director, Center for Technology, Innovation and Competition
University of Pennsylvania Law School
3501 Sansom St.
Philadelphia, PA 19104-6204
(215) 746-8772 (o)
(215) 573-2025 (f)
[email protected]<mailto:[email protected]<mailto:[email protected]%3cmailto:[email protected]>>
http://www.law.upenn.edu/faculty/csyoo/<http://www.law.upenn.edu/faculty/csyoo/>

For more information on the Center for Technology, Innovation and Competition, 
see 
https://www.law.upenn.edu/institutes/ctic/<https://www.law.upenn.edu/institutes/ctic/>.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/82ae6154/attachment-0001.html<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/82ae6154/attachment-0001.html>>

------------------------------

Message: 6
Date: Thu, 3 Jan 2019 22:01:56 +0000
From: Dominik Bay <[email protected]<mailto:[email protected]>>
To: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>
Subject: 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 286, 
3320, 5511, 6461,
6762, 6830, 8220, 9002, 12956
Message-ID: 
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; charset="utf-8"

I see the follwowing ASN transiting a leak concerning 
192.208.19.0/24<http://192.208.19.0/24> originated by 4812

209
286
3320
5400
5511
6327
6461
6762
6830
8218
8220
8447
8551
9002
12956

The proper source is 32982 (Department of Energy).
More details to be found here: 
https://bgpstream.com/event/171779<https://bgpstream.com/event/171779>
And here: 
http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0<http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0>

Cheers,
Dominik




------------------------------

Message: 7
Date: Thu, 3 Jan 2019 14:37:28 -0800
From: Jeff Shultz <[email protected]<mailto:[email protected]>>
To: Dominik Bay <[email protected]<mailto:[email protected]>>
Cc: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>
Subject: Re: 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 
286, 3320, 5511,
6461, 6762, 6830, 8220, 9002, 12956
Message-ID:
<cagb3bgf60fye4w5hwlxqwvv3k06svjmba6hnzjywstrjvzu...@mail.gmail.com<mailto:cagb3bgf60fye4w5hwlxqwvv3k06svjmba6hnzjywstrjvzu...@mail.gmail.com>>
Content-Type: text/plain; charset="UTF-8"

China Telecom originating a network that belongs to the agency that
controls all things nuclear in the US... nothing suspicious there.

On Thu, Jan 3, 2019 at 2:03 PM Dominik Bay 
<[email protected]<mailto:[email protected]>> wrote:
>
> I see the follwowing ASN transiting a leak concerning 
> 192.208.19.0/24<http://192.208.19.0/24> originated by 4812
>
> 209
> 286
> 3320
> 5400
> 5511
> 6327
> 6461
> 6762
> 6830
> 8218
> 8220
> 8447
> 8551
> 9002
> 12956
>
> The proper source is 32982 (Department of Energy).
> More details to be found here: 
> https://bgpstream.com/event/171779<https://bgpstream.com/event/171779>
> And here: 
> http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0<http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0>
>
> Cheers,
> Dominik
>
>


--
Jeff Shultz

--
Like us on Social Media for News, Promotions, and other information!!


<https://www.facebook.com/SCTCWEB/<https://www.facebook.com/SCTCWEB/>>
<https://www.instagram.com/sctc_503/<https://www.instagram.com/sctc_503/>>
<https://www.yelp.com/biz/sctc-stayton-3<https://www.yelp.com/biz/sctc-stayton-3>>
<https://www.youtube.com/c/sctcvideos<https://www.youtube.com/c/sctcvideos>>













_**** This message
contains confidential information and is intended only for the individual
named. If you are not the named addressee you should not disseminate,
distribute or copy this e-mail. Please notify the sender immediately by
e-mail if you have received this e-mail by mistake and delete this e-mail
from your system. E-mail transmission cannot be guaranteed to be secure or
error-free as information could be intercepted, corrupted, lost, destroyed,
arrive late or incomplete, or contain viruses. The sender therefore does
not accept liability for any errors or omissions in the contents of this
message, which arise as a result of e-mail transmission. ****_



------------------------------

Message: 8
Date: Thu, 3 Jan 2019 17:45:00 -0500 (EST)
From: Sean Donelan <[email protected]<mailto:[email protected]>>
To: [email protected]<mailto:[email protected]>
Subject: Astronaut accidently calls 911 from space
Message-ID:
<[email protected]<mailto:[email protected]>>
Content-Type: text/plain; format=flowed; charset=US-ASCII


I was disappointed that it was just a misdial. I was looking forward to
how IP geolocation worked with 9-1-1 calls from space. I always wondered
how that altitude parameter in 911 packets was used. :-)


https://www.newsweek.com/astronaut-accidentally-calls-911-space-1276892<https://www.newsweek.com/astronaut-accidentally-calls-911-space-1276892>



------------------------------

Message: 9
Date: Thu, 3 Jan 2019 18:46:08 -0500
From: Dovid Bender <[email protected]<mailto:[email protected]>>
To: Mark Milhollan <[email protected]<mailto:[email protected]>>
Cc: NANOG <[email protected]<mailto:[email protected]>>
Subject: Re: Cellular backup connections
Message-ID:
<CAM3TTh0mNx4apFpZFTXEzW4=HUM4OQND65gW3f5V2=jtdgp...@mail.gmail.com<mailto:CAM3TTh0mNx4apFpZFTXEzW4=HUM4OQND65gW3f5V2=jtdgp...@mail.gmail.com>>
Content-Type: text/plain; charset="utf-8"

All,

Thanks for all of the feedback. I was on site today and noticed two things.
1) As someone mentioned it could be for static IP's they have the traffic
going to a specific location. The POP is in NJ there was a min. latency of
120ms which prob had to do with this.
2) I was watching the ping times and it looked something like this:
400ms
360ms
330ms
300ms
260ms
210ms
170ms
140ms
120ms
400ms
375ms

It seems to have been coming in "waves". I assume this has to do with "how
cellular work" and the signal. I tried moving it around by putting it down
low on the floor, moving it locations etc. and saw the same thing every
time. I am going to try Verizon next and see how it goes.



On Sat, Dec 29, 2018 at 12:13 PM Mark Milhollan 
<[email protected]<mailto:[email protected]>> wrote:

> On Fri, 28 Dec 2018, Dovid Bender wrote:
>
> >I finally got around to setting up a cellular backup device in our new
> POP.
>
> >When SSH'ing in remotely the connection seems rather slow.
>
> Perhaps using MOSH can help make the interactive CLI session less
> annoying.
>
> >Verizon they charge $500.00 just to get a public IP and I want to avoid
> >that if possible.
>
> You might look into have it call out / maintain a connection back to
> your infrastructure.
>
>
> /mark
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/b4c3f157/attachment-0001.html<http://mailman.nanog.org/pipermail/nanog/attachments/20190103/b4c3f157/attachment-0001.html>>

------------------------------

Message: 10
Date: Fri, 4 Jan 2019 11:21:32 +0300
From: Job Snijders <[email protected]<mailto:[email protected]>>
To: Dominik Bay <[email protected]<mailto:[email protected]>>
Cc: "[email protected]<mailto:[email protected]>" 
<[email protected]<mailto:[email protected]>>
Subject: Re: 192.208.19.0/24<http://192.208.19.0/24> hijack transiting 209, 
286, 3320, 5511,
6461, 6762, 6830, 8220, 9002, 12956
Message-ID:
<CACWOCC8DRPSWCvsa6n-Yyf0LwR=81apcl+havgof9ghwvyh...@mail.gmail.com<mailto:CACWOCC8DRPSWCvsa6n-Yyf0LwR=81apcl+havgof9ghwvyh...@mail.gmail.com>>
Content-Type: text/plain; charset="utf-8"

Dear all,

NTT / AS 2914 deployed explicit filters to block this BGP announcement from
AS 4134. I recommend other operators to do the same.

I’d also like to recommend AS 32982 to remove the AS_PATH prepend on the
/24 announcement so the counter measure is more effective.

Kind regards,

Job

On Fri, Jan 4, 2019 at 1:02 Dominik Bay 
<[email protected]<mailto:[email protected]>> wrote:

> I see the follwowing ASN transiting a leak concerning 
> 192.208.19.0/24<http://192.208.19.0/24>
> originated by 4812
>
> 209
> 286
> 3320
> 5400
> 5511
> 6327
> 6461
> 6762
> 6830
> 8218
> 8220
> 8447
> 8551
> 9002
> 12956
>
> The proper source is 32982 (Department of Energy).
> More details to be found here: 
> https://bgpstream.com/event/171779<https://bgpstream.com/event/171779>
> And here: 
> http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0<http://lg.ring.nlnog.net/prefix_detail/lg01/ipv4?q=192.208.19.0>
>
> Cheers,
> Dominik
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://mailman.nanog.org/pipermail/nanog/attachments/20190104/0c84b757/attachment-0001.html<http://mailman.nanog.org/pipermail/nanog/attachments/20190104/0c84b757/attachment-0001.html>>

End of NANOG Digest, Vol 132, Issue 4
*************************************

Reply via email to