Eric,
My interpretation of the standard is that the grounding conductor needs to
be able to handle the sum of the currents.  If both the supplies are fed
from a common supply, e.g. -48V, then they should both be included in the
calculation.
Regards,
Dave Spencer
Compliance Engineer
Oresis Communications

-----Original Message-----
From: "Meunier, Éric" [mailto:[email protected]]
Sent: Tuesday, March 14, 2000 4:24 PM
To: [email protected]
Subject: Grouding conductor fault current


Hi,
With regards to the GR1089 requirement for a grounding conductor to safely
conduct fault currents "likely to be imposed" (Section 9.7.1, R9-10 [82]):
Do we have to consider that multiple independent outputs of an embedded
power source (ex: 5V and 3.3V) may be shorted simultaneously, or can we
assume that only one would be shorted at a time?

Best Regards,
Eric

===================================