Hi Scott,
It is not necessary to quantify the use data for self-level equipment.  The
racks on hand in CO's are purchased because they meet the requirements of
that installation and the test data for those racks is reviewed just as
rigorously as the data on the equipment that goes into them.  Your mandate
is to ensure that the tests your unit are subjected meet the test criteria. 

For your self-level unit, the intent of the test is to assertion the
operational performance under seismic stress in the worst possible 'typical'
installation.  Consequently, your unit should be placed at the top of an
unequal-flange seismic rack where the deflection is greatest.  The rack, per
GR63 section 5.4.1.3, should be fully loaded with dummy weights to ensure it
duplicates the mass and stiffness of a fully loaded rack.  Additional
weights are place on top of the rack to simulate cable weight.

The test plan should be approved by an RBOC SME, such as Larry Wong or one
of his designates at SBC, prior to running the test.  CA has the biggest
threat and they know what "representative" means to them.  The test report
will show that the unit has been tested with an approved zone 4 rack and
load configuration.

If your test lab doesn't have test plans approved prior to testing, get
another lab.  The going rate for repeating a seismic test is too high to
have to do it twice because someone didn't have a plan approved.

The contact information I have for Larry Wong is a little dated, e.g. no
guarantees:
[email protected]
925 823-4544

Have a Great Day!
Dave Spencer
Oresis Communications

-----Original Message-----
From: Scott Lemon [mailto:[email protected]]
Sent: Wednesday, February 13, 2002 8:35 AM
To: [email protected]
Subject: Re: GR-63 Seismic


This has been my experience too in talking with test labs.  Maybe this is
the generally accepted way?.?.?  Are you guys addressing this in any way in
your user/customer docs (e.g. only tested for compliance in Hendry, model
xyz, etc.)??

Naftali Shani wrote:

> Sounds like the CE + CE = CE?
>
> In my limited experience with the 1 product tested so far NOT in its
> normally installed rack, the lab did just that (generic Hendry).
>
> Regards,
> Naftali Shani, Catena Networks (www.catena.com)
> 307 Legget Drive, Kanata, Ontario, Canada K2K 3C8
> 613.599.6430/866.2CATENA (X.8277); C 295.7042; F 599.0445
> E-mail: [email protected]
>
>  -----Original Message-----
> From:   Scott Lemon [mailto:[email protected]]
> Sent:   Wednesday, February 13, 2002 10:19 AM
> To:     Nebs (E-mail)
> Subject:        GR-63 Seismic
>
> Greetings Nebs group,
>
> I am interested in the general consensus with respect to one aspect of
> seismic testing of rack mounted equipment....
>
> If a shelf-based system, which is designed to be installed in any
> seismic approved rack assembly (e.g. 19"), is seismic tested in a
> particular rack (e.g. Newton), is the performance normally extrapolated
> to be representative of installation in any generally "seismic approved"
> 19" rack (e.g. Hendry, tested by rack manuf with dummy loads, etc.)??
> In other words, is GR-63 seismic compliance for the shelf system linked
> only to the rack in which it was tested, or will any generally tested
> GR-63 "seismic approved" rack suffice?
>
> Any and all opinions welcome.
>
> Thanks,
> Scott
>
> --
> Regards,
>
> Scott Lemon
> CASPIAN NETWORKS
> [email protected]
> www.caspiannetworks.com

Reply via email to