Hello John,

The heat dissipation should be calculated from measurements, not from maximum 
ratings.  It is most common for the input into the equipment to be -52.6 VDC as 
this is the standard float voltage in C.O.'s.  It probably is not a big deal if 
you use -48 VDC, you will just have higher current.  You must
also subtract any power that is dissipated in OSP cables, and remote equipment 
such as phones, span powered remotes, etc.  You must also add in any power that 
may be dissipated by the equipment that comes from other equipment on telecom 
or other types of ports.  An example is an FXO card which sinks
current from an FXS or other POTS line.  Another example is sealing current, if 
your equipment "sinks" sealing current on an interface such as ISDN, DDS,  T1, 
HDSL, etc., you need to add it to your equipment's heat dissipation.  Remember 
that if you "source" sealing current or span power, you need
to subtract the power sent to other equipment, it is dissipated elsewhere such 
as remotely or in the footprint of other equipment in the C.O.

POTS interfaces can be tricky though as the power dissipated in each interface 
can vary radically with its on-hook/off-hook state (almost 0 watts on-hook, and 
.5 to a couple watts off-hook).  If you are testing FXO's, you also can have 
drastic differences if the POTS interface feeding it is a
constant voltage (old step x  step switch or older FXS) or a constant current 
(newer electronic switch, PBX, FXS's, etc.).  Taking all the ports off-hook at 
the same time will give you a worst case scenario, but that is rarely 
representative of reality.  Most customers can provide you with the CCS
number that you need to use.  The CCS number helps you determine the percentage 
of off hook/ringing/active POTS lines at any given time.  We have seen 
typically that range to be 17% to 50%.  We typically have the labs make the 
calculations at 17%, 50%, and 100%, this way the end customer can
interpolate the heat dissipation based on typical loads.  I believe all 
customers allow you to assume constant current switches, FXS's, PBX's now.

For non-POTS interfaces and equipment the calculations are typically much 
easier as the wattage does not vary much with load.  One technology to be 
careful of is ADSL though.  It varies substantially with cable length and 
whether it is trained (sync'd) with a remote or not trained.  Most other DSL's
have the same or similar heat dissipation even if not sync'd. 

Good Luck,

Jim

Jim Wiese
NEBS Project Manager/Compliance Engineer
ADTRAN, INC.
901 Explorer Blvd.
P.O. Box 140000
Huntsville, AL 35814-4000
256-963-8431
256-963-8250 fax
jim.wi...@adtran.com 



-----Original Message-----
From: John Loiselle [mailto:jloise...@integralaccess.com]
Sent: Monday, October 14, 2002 8:48 AM
To: nebs@world.std.com
Subject: Equipment Area Heat Release Objective


Hello,
I am requesting information to help me obtain a better understanding of the
requirements called out in GR-63, 4.1.4, R4-11, O4-12, O4-13, and Table 4-6.
I have a "shelf" equipment configuration with the following Assumptions
noted in the report:

Rack depth (Rd) is 1 ft.
Rack width (Rw) is 2.17ft.
Maintenance aisle depth (Md) is 2.5 ft.
Wiring aisle depth (Wd) is 2 ft.
Height of equipment is 2ft.
Maximum operating voltage (V) is 48VDC.
Maximum operating current (A) is 23.4.

My report states that I do not conform to O4-12. The calculated Heat
Dissipation was 80W/ft2/ft (2790W/m2/m).

Since more than half the current draw is derived from POTS (all phones being
off hook at the same time), I am curious if the 23.4A is the correct number
to use for this calculation.  It appears that the heat would not be
dissipated inside the enclosure but at the other end of the cable (phone?).
When I see various TDM enclosures, they are physically smaller and the port
density is greater.  How are these enclosures allowed to fill a rack in one
bay?  Is there allowances taken for POTS configurations?  Thanks.  Regards,
John Loiselle
Regulatory Compliance
Integral Access, Inc.
ph (978) 367 7585