Good morning Roger,
You will find attached the text files with the commands of our 4 products EPYC:
gtec.NEON.txt, gtec.QUANTUM.txt, gtec.ION.txt and gtec.TETRYS.txt.
We look forward to your kind reply that the files sent are correct, thanks.
Marika Rigon
Marketing Department
Email: [email protected]
-----Messaggio originale-----
Da: Roger Price <[email protected]>
Inviato: venerdì 16 luglio 2021 10:32
A: Marika Rigon <[email protected]>
Cc: [email protected]
Oggetto: Re: R: [Nut-upsdev] [HCL] <EPYC> <UPS> supported by <usbhid-ups -Cyber
Power>
Hello Marika, Yes, those are the data values we need. To put them in the
database, we will need them as text files. This could be done with the
commands shown below which will produce 4 files: gtec.NEON.txt,
gtec.QUANTUM.txt, gtec.ION.txt and gtec.TETRYS.txt.
Could you run the commands and send us the four files? Thanks, Roger
Using a NEON series UPS:
echo G-Tec NEON > gtec.NEON.txt
upsc <ups> >> gtec.NEON.txt
upsrw <ups> >> gtec.NEON.txt
upscmd -l <ups> >> gtec.NEON.txt
Using a QUANTUM series UPS:
echo G-Tec QUANTUM > gtec.QUANTUM.txt
upsc <ups> >> gtec.QUANTUM.txt
upsrw <ups> >> gtec.QUANTUM.txt
upscmd -l <ups> >> gtec.QUANTUM.txt
Using an ION series UPS:
echo G-Tec ION > gtec.ION.txt
upsc <ups> >> gtec.ION.txt
upsrw <ups> >> gtec.ION.txt
upscmd -l <ups> >> gtec.ION.txt
Using a TETRYS series UPS:
echo G-Tec TETRYS > gtec.TETRYS.txt
upsc <ups> >> gtec.TETRYS.txt
upsrw <ups> >> gtec.TETRYS.txt
upscmd -l <ups> >> gtec.TETRYS.txt
There is help for this operation at
https://www.windowscentral.com/how-save-command-output-file-using-command-prompt-or-powershell
On Thu, 15 Jul 2021, Marika Rigon wrote:
> Good morning Roger,
>
> Here is an example of NUT command test screenshot for City800(QUANTUM). Is
> this what you need?
> If yes, we will send the same command test screenshot for NEON, QUANTUM, ION
> and TETRYS.
> We should only pick one model form each series to do the test, right?
> Example: Is enough for NEON series (650 VA, 850 VA, 1000 VA) to send you only
> the NUT commands of NEON 650 VA?
>
> Looking forward to your reply, thanks.
>
> Marika Rigon
> Marketing Department
> Email: [email protected]
G-Tec ION
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: 1
battery.runtime: 3600
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 135.0
battery.voltage.nominal: 120
device.mfr: 1
device.model: 600
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: Windows-v2.6.5-5-7-g72f380c
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 270
input.transfer.low: 180
input.voltage: 4.1
input.voltage.nominal: 230
output.voltage: 234.5
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: 1
ups.model: 600
ups.productid: 0601
ups.realpower.nominal: 360
ups.status: OL
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 270
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 180
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30
Instant commands supported on UPS [ION600]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
G-Tec TETRYS
battery.charge: 38
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: 1
battery.runtime: 1320
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 12.5
battery.voltage.nominal: 12
device.mfr: 1
device.model: 650
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: Windows-v2.6.5-5-7-g72f380c
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 29
input.transfer.low: 17
input.voltage: 5.0
input.voltage.nominal: 230
output.voltage: 235.4
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: 1
ups.model: 650
ups.productid: 0601
ups.realpower.nominal: 360
ups.status: OL CHRG
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 29
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 17
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30
Instant commands supported on UPS [Tetrys650]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
G-Tec NEON
battery.charge: 50
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: 1
battery.runtime: 300
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 72.0
battery.voltage.nominal: 72
device.mfr: 1
device.model: UPS-USBAdaptor
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: Windows-v2.6.5-5-7-g72f380c
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 14
input.transfer.low: 9
input.voltage: 25.2
input.voltage.nominal: 102
output.voltage: 123.4
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 5
ups.mfr: 1
ups.model: UPS-USBAdaptor
ups.productid: 0601
ups.realpower.nominal: 999
ups.status: OL BOOST
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 14
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 9
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30
Instant commands supported on UPS [Neon1000]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
G-Tec QUANTUM
battery.charge: 42
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date:
battery.runtime: 3000
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 271.0
battery.voltage.nominal: 120
device.mfr: CPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: Windows-v2.6.5-5-7-g72f380c
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 36
input.transfer.low: 180
input.voltage: 0.0
input.voltage.nominal: 230
output.voltage: 232.4
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: CPS
ups.productid: 0601
ups.realpower.nominal: 2200
ups.status: OB DISCHRG
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 36
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 180
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30
Instant commands supported on UPS [QUANTUM2200]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test