Jim Klimov <[email protected]> > > I believe some fixes were applied to the branch since your report (most > visibly, about battery time settings), are you in position to test how it > behaves now? :)
Hi: I got another ups for testing. so I test the new commit for both APC SRT3000XL and SMT2200RM2U. the results below: 1. I get the new attribute "ups.test.result" for both ups and it is fine. 2. upsrw battery.date works fine for both UPS. and the modified result shows immediately. no need to restart the driver. (I still need to restart the driver to get correct battery.date.maintenance. but I think that's not very important. there's not even that attribute at apcupsd.) 3. test.battery.stop works fine at SRT3000XL. but it is not working at SMT2200RM2U (same experience as the driver author). I think it is not important. BTW, at program "apctest" from apcupsd, the function "test.battery.start" is called "self test", and the physical ups panel also shows "self test". the function "test.panel.start" is called "alarm test" at apctest. what bothers me is when testing, the ups status will become "OB TEST". "OB" will cause the system shutdown when I configured upssched for early shutdown. I had only saw one very old APC ups which will show "OB" when testing/calibration. most will show like "OL DISCHRG". but I think the information is from ups and can not change? 4. almost all the power-related upscmd command(load.* outlet.* shutdown.*) are not working. there is only one exception: ouetlet1.* works at SMT2200RM2U (I test outlet.1.load.off). nothing works at SRT3000XL. the new driver detect there are two outlet groups for both UPS(outlet.group.count: 2). but SMT2200RM2U has only one outlet group. since the new driver can not shutdown the ups, I wonder what's the fastest method to test the function (previously I setup the ups and unplug the utility from the ups for testing). is "upsrw driver.flag.allow_killpower=1" then "upscmd driver.killpower" the correct testing procedure? 5. the default/actual shutdown delay for both ups is 90 seconds(when real testing under apcupsd). the "upsrw -l myups" has value "90" for the attribute "outlet.group.1.delay.shutdown". but other attributes related to the shutdown delay are all "0". BTW, apcupsd also shows "0" shutdown delay although it can correctly shutdown ups. below are the raw data for SMT2200RM2U: >upsc myups battery.charge: 100.00 battery.date: 2023-11-25 battery.date.maintenance: 2028-05-25 battery.runtime: 22320 battery.temperature: 24.69 battery.voltage: 54.53 device.mfr: American Power Conversion device.model: Smart-UPS 2200 device.serial: AS1848260180 device.type: ups driver.debug: 0 driver.flag.allow_killpower: 0 driver.name: apc_modbus driver.parameter.pollinterval: 10 driver.parameter.port: /dev/ttyS0 driver.parameter.synchronous: yes driver.state: quiet driver.version: 2.8.1.1 driver.version.internal: 0.10 experimental.output.energy: 0 input.transfer.high: 127 input.transfer.low: 106 input.transfer.reason: AcceptableInput input.voltage: 109.39 outlet.group.0.delay.reboot: 8 outlet.group.0.delay.shutdown: 0 outlet.group.0.delay.start: 0 outlet.group.0.name: UPS Outlets outlet.group.1.delay.reboot: 8 outlet.group.1.delay.shutdown: 90 outlet.group.1.delay.start: 0 outlet.group.1.name: Outlet Group 1 outlet.group.2.delay.reboot: -1 outlet.group.2.delay.shutdown: -1 outlet.group.2.delay.start: -1 outlet.group.2.name: outlet.group.3.delay.reboot: -1 outlet.group.3.delay.shutdown: -1 outlet.group.3.delay.start: -1 outlet.group.3.name: outlet.group.count: 2 output.current: 0.00 output.frequency: 59.95 output.voltage: 109.39 ups.delay.reboot: 8 ups.delay.shutdown: 0 ups.delay.start: 0 ups.efficiency: LoadTooLow ups.firmware: UPS 15.0 ups.id: APCUPS ups.load: 0.00 ups.mfr: American Power Conversion ups.mfr.date: 2018-11-26 ups.model: Smart-UPS 2200 ups.power: 0.00 ups.power.nominal: 2200 ups.realpower: 0.00 ups.realpower.nominal: 1980 ups.serial: AS1848260180 ups.status: OL HE ups.test.result: Passed, Source: Protocol ups.timer.reboot: -1 ups.timer.shutdown: -1 ups.timer.start: -1 >upsrw -l myups [battery.date] Battery change date Type: NUMBER Value: 2023-11-25 [driver.debug] Current debug verbosity level of the driver program Type: NUMBER Value: 0 [driver.flag.allow_killpower] Safety flip-switch to allow the driver daemon to send UPS shutdown command (accessible via driver.killpower) Type: NUMBER Value: 0 [input.transfer.high] High voltage transfer point (V) Type: NUMBER Value: 127 [input.transfer.low] Low voltage transfer point (V) Type: NUMBER Value: 106 [outlet.group.0.delay.reboot] Description unavailable Type: NUMBER Value: 8 [outlet.group.0.delay.shutdown] Description unavailable Type: NUMBER Value: 0 [outlet.group.0.delay.start] Description unavailable Type: NUMBER Value: 0 [outlet.group.0.name] Description unavailable Type: STRING Maximum length: 16 Value: UPS Outlets [outlet.group.1.delay.reboot] Description unavailable Type: NUMBER Value: 8 [outlet.group.1.delay.shutdown] Description unavailable Type: NUMBER Value: 90 [outlet.group.1.delay.start] Description unavailable Type: NUMBER Value: 0 [outlet.group.1.name] Description unavailable Type: STRING Maximum length: 16 Value: Outlet Group 1 [outlet.group.2.delay.reboot] Description unavailable Type: NUMBER Value: -1 [outlet.group.2.delay.shutdown] Description unavailable Type: NUMBER Value: -1 [outlet.group.2.delay.start] Description unavailable Type: NUMBER Value: -1 [outlet.group.2.name] Description unavailable Type: STRING Maximum length: 16 Value: [outlet.group.3.delay.reboot] Description unavailable Type: NUMBER Value: -1 [outlet.group.3.delay.shutdown] Description unavailable Type: NUMBER Value: -1 [outlet.group.3.delay.start] Description unavailable Type: NUMBER Value: -1 [outlet.group.3.name] Description unavailable Type: STRING Maximum length: 16 Value: [ups.delay.reboot] Interval to wait before rebooting the UPS (seconds) Type: NUMBER Value: 8 [ups.delay.shutdown] Interval to wait after shutdown with delay command (seconds) Type: NUMBER Value: 0 [ups.delay.start] Interval to wait before (re)starting the load (seconds) Type: NUMBER Value: 0 [ups.id] UPS system identifier Type: STRING Maximum length: 16 Value: APCUPS >upscmd -l myups beeper.mute - Temporarily mute the UPS beeper bypass.start - Put the UPS in bypass mode bypass.stop - Take the UPS out of bypass mode calibrate.start - Start run time calibration calibrate.stop - Stop run time calibration driver.killpower - Tell the driver daemon to initiate UPS shutdown; should be unlocked with driver.flag.allow_killpower option or variable setting driver.reload - Reload running driver configuration from the file system (only works for changes in some options) driver.reload-or-error - Reload running driver configuration from the file system (only works for changes in some options); return an error if something changed and could not be applied live (so the caller can restart it with new options) driver.reload-or-exit - Reload running driver configuration from the file system (only works for changes in some options); exit the running driver if something changed and could not be applied live (so service management framework can restart it with new options) load.off - Turn off the load immediately load.off.delay - Turn off the load with a delay (seconds) load.on - Turn on the load immediately load.on.delay - Turn on the load with a delay (seconds) outlet.0.load.cycle - Description unavailable outlet.0.load.off - Description unavailable outlet.0.load.on - Description unavailable outlet.0.shutdown.return - Description unavailable outlet.1.load.cycle - Description unavailable outlet.1.load.off - Turn off the load on outlet 1 immediately outlet.1.load.on - Turn on the load on outlet 1 immediately outlet.1.shutdown.return - Turn off the outlet 1 and return when power is back outlet.2.load.cycle - Description unavailable outlet.2.load.off - Turn off the load on outlet 2 immediately outlet.2.load.on - Turn on the load on outlet 2 immediately outlet.2.shutdown.return - Turn off the outlet 2 and return when power is back outlet.3.load.cycle - Description unavailable outlet.3.load.off - Description unavailable outlet.3.load.on - Description unavailable outlet.3.shutdown.return - Description unavailable shutdown.reboot - Shut down the load briefly while rebooting the UPS shutdown.reboot.graceful - Delay briefly then shut down the load while rebooting the UPS shutdown.return - Turn off the load and return when power is back shutdown.stayoff - Turn off the load and remain off test.battery.start - Start a battery test test.battery.stop - Stop the battery test test.panel.start - Start testing the UPS panel _______________________________________________ Nut-upsdev mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev