On Jan 2, 2024, at 1:49 PM, Kelly Byrd <[email protected]> wrote:
> 
> My question for you all is what units ups.powersummary.runtimetoempty is 
> supposed to be in? This doc from USB.org: 
> https://www.usb.org/sites/default/files/hut1_4.pdf (Section 31.2) says 
> minutes,

Do you mean the Power Device Class documentation?

I agree that the description on p.37 of 
https://usb.org/sites/default/files/pdcv11.pdf says minutes, but the last 
reference to RunTimeToEmpty on p.57 is embedded in a descriptor that specifies 
the units to be seconds. I think most manufacturers end up reporting seconds, 
since the descriptors tend to look fairly similar to the spec.

> Is this just a case where real world UPS' are using seconds so we're stuck 
> with it now?

That, and the fact that that the HID protocol uses a lot of base SI units.

> I guess it's being pedantic, but IMO trying to measure a UPS remaining 
> runtime with accuracy is sort of silly. I noticed this because I'm cobbling 
> together a personal project that has absurd capacity for the load, somewhere 
> around 2-3 days from a fully charged battery and I'm using NUT's Arduino 
> driver to report things.

To be honest, this is exactly the sort of thing that the Physical and Logical 
units are meant to address. You can keep the internal time-remaining counter in 
whatever format makes sense in the firmware, and specify some Logical units to 
map that back to seconds so you aren't sending 32-bit numbers for something 
with a really small range.

I'm pretty sure there is one UPS where the shutdown timer settings are kept in 
minutes, and the NUT drivers expose seconds because the vendor specified a 
Physical-to-Logical factor of 60.

- Charles