I'm unsure about the intended semantic of test.battery.start.deep and 
calibrate.start.

The Masterguard UPSen I wrote nutdrv_qx_masterguard for provide, apart from the 
usual ten-second (T) and n-Minute (Tn) battery tests, a "Test until battery 
low" (TL) as well as a "Test until battery is depleted" command.

TL will, according to my experiment, stop around 20% (or 10 minutes left), TUD 
will only stop at 0%.
The description of TUD suggests it's for battery ageing factor calibration.

Is it OK to use test.battery.start.deep for TL and calibrate.start for TUD?

The way to stop TUD seems to be CT, the same as to stop T, Tn and TL.
Is it OK to issue CT for calibrate.stop, e.g. doing the same thing as for 
test.battery.stop?

The attached patch would implement this (NB: the current 
test.battery.start.deep doesn't work as I forgot TUD needs the "slave address" 
in the command).
--- drivers/nutdrv_qx_masterguard.c.orig        2024-06-06 17:49:08.971092263 
+0200
+++ drivers/nutdrv_qx_masterguard.c     2024-06-06 17:51:12.001081299 +0200
@@ -864,11 +864,11 @@ static item_t masterguard_qx2nut[] = {
        /* test.failure.stop */
        { "test.battery.start",         0,      NULL,   NULL,           "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   masterguard_test_battery },
        { "test.battery.start.quick",   0,      NULL,   "T\r",          "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
-       { "test.battery.start.deep",    0,      NULL,   "TUD\r",        "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
+       { "test.battery.start.deep",    0,      NULL,   "TL\r",         "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
        { "test.battery.stop",          0,      NULL,   "CT\r",         "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
        /* test.system.start */
-       /* calibrate.start */
-       /* calibrate.stop */
+       { "calibrate.start",            0,      NULL,   "TUD,XX\r",     "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    
masterguard_add_slaveaddr,      NULL,   NULL },
+       { "calibrate.stop",             0,      NULL,   "CT\r",         "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL }, /* same as test.battery.stop */
        { "bypass.start",               0,      NULL,   "FOFF\r",       "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
        { "bypass.stop",                0,      NULL,   "FON\r",        "",     
0,      '\0',   "",     0,      0,      NULL,   QX_FLAG_CMD,    NULL,           
                NULL,   NULL },
        /* reset.input.minmax */
_______________________________________________
Nut-upsdev mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to