Arjen de Korte wrote:
>> I'm just looking at the code of snmp-ups driver in the source tree.
>> I'm trying to find out, what can I change in the code to force the
>> snmp-ups driver to send shutdown command to the upsd to shutdown the
>> computer when I set up on the UPS via telnet that it should restart
>> gracefully.
>
> The 'upsd' server sits between (in your case) the snmp-ups driver and
> (usually) upsmon client. The latter will shutdown the system if it sees
> that the UPS is both reporting On Battery (OB) and Low Battery (LB) or
> when the Force ShutDown (FSD) flag is set. Since drivers should *never*
> set the FSD flag directly, your only option here is to make the snmp-ups
> driver reports both OB and LB. Any clients attached should respond to this
> by shutting down.
>
> Best regards, Arjen
Many thanks for help.
I have now apccmib.h
#define APCC_OID_POWER_STATUS ".1.3.6.1.4.1.318.1.1.1.4.1.1.0"
/* Defines for APCC_OID_POWER_STATUS */
info_lkp_t apcc_pwr_info[] = {
{ 1, "" }, /* unknown */
{ 2, "OL" }, /* onLine */
{ 3, "OB" }, /* onBattery */
{ 4, "BOOST" }, /* onSmartBoost */
{ 5, "OFF" }, /* timedSleeping */
{ 6, "OFF" }, /* softwareBypass */
{ 7, "OFF" }, /* off */
{ 8, "OB LB" }, /* rebooting */
{ 9, "BYPASS" }, /* switchedBypass */
{ 10, "BYPASS" }, /* hardwareFailureBypass */
{ 11, "OFF" }, /* sleepingUntilPowerReturn */
{ 12, "TRIM" }, /* onSmartTrim */
{ 0, "NULL" }
} ;
Is this what you were talking about? I have no other idea what else to
do looking at the code.
Best regards, Tomas
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev