On Fri, Jun 13, 2008 at 3:11 PM, Chris Adams <[EMAIL PROTECTED]> wrote:
> I had a power hiccup yesterday and a server connected to a Best Ferrups
> 18KVA shutdown.  The problem is that the UPS is reporting remaining
> runtime in minutes but nut treats it as seconds (so nut thought it only
> had 46 seconds left).

The patch looks good at first glance, but by default, NUT should not
use the runtime estimate to initiate a shutdown.

Are you using upssched? Any special parameters to the driver?

Otherwise, NUT will shut down when the UPS signals LB (low battery),
which is a unit-less boolean value.

-- 
- Charles Lepple